Hi everybody,

Will anybody be able to help me out with this question? Regarding locations containing a bath or shower, additional protection by RCDs to regulation 415.1.1 of the 17th edition regs states. The use of RCD with a current rating not exceeding 30 mA and an operating time not exceeding 40ms at residual current of 5 1Δn.

Is this telling me that the reading on my meter when testing the RCD covering the circuit is less than 40ms on the x5 setting?

Thanks in advance for any advice on the matter.
 
  • Useful
Reactions: Dazza1976
for most applications, a 30mA RCD must trip in <40mSec. @ 5 x Δn. bathrom is no exceptoin.
 
1Δ within 300ms on both 0° and 180° with the highest recorded.
5Δ within 40ms on both 0° and 180° with the highest recorded.
 
  • Agree
Reactions: Davisonp
and then there's RCDs on TT systems.
 
Hi everybody,

Will anybody be able to help me out with this question? Regarding locations containing a bath or shower, additional protection by RCDs to regulation 415.1.1 of the 17th edition regs states. The use of RCD with a current rating not exceeding 30 mA and an operating time not exceeding 40ms at residual current of 5 1Δn.

Is this telling me that the reading on my meter when testing the RCD covering the circuit is less than 40ms on the x5 setting?

Thanks in advance for any advice on the matter.
 

Attachments

  • Like
Reactions: Wilko
and then there's RCDs on TT systems.
And then there are GFCIs wonder how or if they ever test them in septic land? they just seem to bung em in willy nilly.
 
  • Like
Reactions: timbobelfast
Seeing's though we're all getting a bit picky - its Xmas, peace on earth, good will to all men & all that :); the OP's title is referenced by reg 701.411.3.3. Which itself refers to reg 415.1.1. using them thereof. The aforementioned reg, refers to low voltage circuits. Just getting in practise for me 18th exam, book reading skills.

'What's it all about Alfie slightly/clueless'?
 
  • Like
Reactions: Dave OCD

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Shower Location Question
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
slightly/clueless,
Last reply from
Midwest,
Replies
10
Views
1,930

Advert