H

horsleya

I am hoping to use my own house for my assessment to join either NICEIC/Elecs/NAPIT however I have a question over the size of the earth conductor.

Most people give me the stock answer of 16mm as the Tails are 25mm however I do not believe that this has to apply to a TT system although I am happy to be proven wrong.
542.3.1 refers to 543 which in turn states that I can calculate the CSA based on the adiabatic equation in 543.1.3. I am no expert on this equation so I would love to see someone work this through or let me know what they believe the values should be.

I have a Ze reading of 36 Ohms however when the Main Potential Bonding is connected my Zs drops to 26 Ohms (Parallel Paths). Therefore my PFC is 9amps and this checks out with my tester (I have rounded the figure up for this message).

As I currently have a 10mm cable about 3M long going to the Earth rod I believe that this is OK. The cable is above ground and although currently exposed I intend to enclose it in plastic conduit.

Am I missing something?
What should value t be in the equation? Should it be 0.2 from table 41.1 on page 46?
 
Main Earthing Conductor


The minimum csa of the main earthing conductor must be determined by the adibiatic equation or selected from Table 54.7 543.1.1.
If the adibiatic equation is used, the minimum csa of the main earthing conductor must be 6mm 544.1.1.
Table 54.7 suggests a 16mm main earthing conductor for phase conductors with a csa of up to 35mm.

Adibiatic Equation


The c.s.a. of all protective conductors (excluding protective bonding conductors) can
be calculated using the adibiatic equation. 543.1.1


adi2.jpg


S is the minimum c.s.a. of the c.p.c. I is the fault current (230v / Zs) measured in Amps


t is the disconnection time of the protective device (see figs 3.1 - 3.6 p244 - 251).

k is a factor taken from the tables 54.2 to 54.6 p129, p130.
 
Last edited:
At the risk of demonstrating a lack of knowledge on the adiabatic equation I will have an attempt:

I=9A (My PFC)
T=0.2 (Taken from table 41.1 on page 46)
k=143 (Taken from Table 54.2 on page 129)

Therefore square root of (9*9*0.2) = 4.0249
16.2 / 143 = 0.028 CSA

This looks far too low but I guess that this is due to the high resistance of an earth rod and hense the low PFC.

Any comments? Have I used the correct Values? Have I made a fool of myself?
 
I posted my second post before seeing Sintra's reply so I will quickly check over what you have said and see if I was too far off.

Thanks for the quick reply
 
Last edited by a moderator:
Surely your PFC should be 900A not 9A
 
Your calculation is however correct for the figures you have used.
 
My prospectic short circuit current is naturally much higher but the prospectic Fault Current on the earth rod is definately 9A.

The Zs is 26 Ohms. 230/26 = 9 (Roughly).

As the Earthing conductor is only applicable under fault conditions I would have thought that this is what I should be using?
 
Last edited by a moderator:
My prospectic short circuit current is naturally much higher but the prospectic Fault Current on the earth rod is definately 9A.

The Zs is 26 Ohms. 230/26 = 9 (Roughly).

As the Earthing conductor is only applicable under fault conditions I would have thought that this is what I should be using?


Appologies I didn't read the values in 1st post correctly.
 

Reply to Size of Conductor for TT Installation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
280
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Don't come across this very often - but I've had a CU delivered for a caravan job (not static btw), and it's been supplied with a neutral...
Replies
7
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
436
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
522

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock