depends..is the detector cabling fused dowm accordingto it's csa?
 
unconventional but can't see any reg. being broke.
 
If it is a ring final circuit it requires suitable circuit protection to BS1363.
 
Last edited:
560.10 states 5839(-6) should be complied with;

15.4.a.i. states an independent circuit is permitted.

15.4.a.ii states a local lighting circuit is permissible

The above described Installation is neither, therefore does not meet 5839-6 and as such 560.10 is not complied with.

HOWEVER the installer can list it as a deviation from standard and it would them comply with 560.10 however the liability is on the installer should something go wrong or the system not function.
 
It is not my area, so I looked up the instructions for the Aico Ei140RC out of curiosity and was a little surprised to see no mention of maximum OCPD limits!

I would have though something like a 10A MCB (typical maximum for lights) would be specified, but nope....
 
BS5839:1 or 6 is generally not concerned with circuit protection just compliance with BS7671 is maintained however it does suggest circuit configuration.
 

Reply to Smoke detector wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been covered before, but wondering if any amendments recently. I’ve been asked to fit detectors in a bungalow holiday cottage. Just over the...
Replies
0
Views
646
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
317
Good morning, I'm in the process of a partial refurbishment which will involve the present kitchen being changed into a bedroom instead and the...
Replies
3
Views
898
I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
2K
I'm about to order this wired smoke alarm system as it can network but I just went to see how my existing fire alarms are hooked up and there...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock