A bit of advice is needed chaps , got called to a house today to complete spoitlights that the owner had started basicly he marked out and cut the holes out where he wanted the lights and wanted me to wire up the lights he got from BBQ they are 12v 25w halogens. problem is that one of the spotlights just missed a joist and is about 10mm from it , i need to know is there anything i can do to stop the heat getting to the joist ? As a last resort i know ill have to redo his holes , but i can help it i dont want that. any suggestions ?
thanks alot.
 
can you blank that 1 off without the pattewn then looking like a dog's breakfast, or move it a few inches and patch the original hole?
 
Personally i would move it. There will be a min distance in the instructions that they have to be installed from joists etc.

The other option is to replace them with main fittings and LEDs
 
A bit of advice is needed chaps , got called to a house today to complete spoitlights that the owner had started basicly he marked out and cut the holes out where he wanted the lights and wanted me to wire up the lights he got from BBQ they are 12v 25w halogens. problem is that one of the spotlights just missed a joist and is about 10mm from it , i need to know is there anything i can do to stop the heat getting to the joist ? As a last resort i know ill have to redo his holes , but i can help it i dont want that. any suggestions ?
thanks alot.

Is the rest of the light exposed and able to disapate the heat into free air, can the transformer be place away from the beam? If so, I'd be tempted to just fit it.
Moving lights adjusting the pattern etc would be a nightmare!
 
I had a similar one to this and fitted some supalux to the joist as protection. Checked back on it several times and no sign of heat damage so I guess its doing its job.
 
  • Like
Reactions: 1 person
Thanks for the quick reply gents , i could move the fitting but it would mean moving the other 5 too , to keep them looking inline , the fitting has free air all around apart from the joist ,
 
Personally i would move it. There will be a min distance in the instructions that they have to be installed from joists etc.

The other option is to replace them with main fittings and LEDs

would i be able to swap like for like from halogen to LEDs , is guessing this is because LEDS give of less heat ?
 
would i be able to swap like for like from halogen to LEDs , is guessing this is because LEDS give of less heat ?

A lot lot less, but reading the suggestions posted by others regarding covering the timber with some kind of heat barrier, it would be another solution.

Never thought of using products like that to protect joinst/timbers before.
 
I would probably fit a fire hood and leave well alone,
I have seen lots of 50w gu10s and mr16 fittings near touching joists and they have been fine, not what I would do nor recomend doing but if the holes are already cut and ceiling decorated you options are a bit limited.
 
The way I would look at the problem
Ask myself why should they be apart from the beams,conclusion,they can cook them and possibly cause a fire
Given that the damage has been done,the hole has been cut,the solution would be to make it so that heat damage will not occur
Led lamps or
I would insulate the beam with heat retardent material,a little bit of Welsh slate tacked on there should do the trick

On a further point,it would take some enormous heat source to set fire to the side of a beam
If the heat build up was that intense,the cable would likely melt and the light would go out before beam damage.or at least that would be my reckoning
 
How about getting 1 of those heat resistant pads that plumbers use when soldering near tiles etc and using that to deflect heat away from the joist. Maybe someones already mentioned that here.......
 
If the fitting has an F without a bar across it then it CAN be fixed within combustible material (wood, MDF etc) if it has a cross within the F and trianlge then it must not be installed within combustible material. Another option is to get a fire hood. Page 150 in the 17th edition.
 
Thanks for the tips guys i went with using the plumbers heat pad , only £3 from the wholesalers bit of a bargin me thinks :D

A reasonable solution to a dodgy problem. (and it was my suggestion! I'm skint so there's no point in suing me)
My only concern is that, are you doing a minor works cert with the knowledge that there is a dubious bit of installation going on, ie, light fitting installed not to manufacturers specs & you know it's too close to a joist???
 
Last edited by a moderator:
A reasonable solution to a dodgy problem. (and it was my suggestion! I'm skint so there's no point in suing me)
My only concern is that, are you doing a minor works cert with the knowledge that there is a dubious bit of installation going on, ie, light fitting installed not to manufacturers specs & you know it's too close to a joist???

You bring up an extremely interesting point regarding how far people should go in bending the rules. I guess it boils down to how badly the individual in question needs the work? Stick rigidly to them and risk losing the work, or be flexible and possibly have some worry :uhoh2:
No doubt in these cases, if a property was damaged in anyway due to rule bending, the owner would be after you like a shot.

I guess when work is plentyful, walking away from recalcitrant owners is rather easier :yes:
 
I think thats a perfect solution for the problem using the plumbers heat pad. Install it well and I wouldn't worry about it anymore. Seen a couple of joists notched out to get the lights it and never noticed any charring on the wood.
 
I think thats a perfect solution for the problem using the plumbers heat pad. Install it well and I wouldn't worry about it anymore. Seen a couple of joists notched out to get the lights it and never noticed any charring on the wood.

I've got disagree on that statement.

The regs specifically state that equipment should be installed to manus specs, in this case xxmills gap etc. so it is a botch job.
There is so much chit chat on here about doing monkey work, diy efforts are going to burn your house down, it's your name on the documentation etc etc etc...the OP should just so NO.

Or just do it, sign nothing and take the money and run :-)
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Spot light question
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
26
Unsolved
--

Advert

Thread statistics

Created
liambroad,
Last reply from
Engineer54,
Replies
26
Views
2,783

Advert