Hi all,
I have an fcu feeding a washing machine in the kitchen, is it ok to run a spur from the fcu to feed an external socket on the other side of the wall? I know its notifiable work, i have passed my 2382 and am hoping to get niceic approval in the next month or so. I figure running the spur from the fcu will offer more protection than just running it from the socket? Thoughts??

Down2earth
 
Hi all,
I have an fcu feeding a washing machine in the kitchen, is it ok to run a spur from the fcu to feed an external socket on the other side of the wall? I know its notifiable work, i have passed my 2382 and am hoping to get niceic approval in the next month or so. I figure running the spur from the fcu will offer more protection than just running it from the socket? Thoughts??

Down2earth

Providing the FCU is on the ringmain then yeah that would be ok, don't spur off the washing m/c socket!
 
A spur from a spur is not allowed, unless it is fused, and also a good idea to run the new feed in 4mm cablefrom the ring.
Get yoour self a copy of the onsite guide and the big red book :)
 
A spur from a spur is not allowed, unless it is fused, and also a good idea to run the new feed in 4mm cablefrom the ring.
Get yoour self a copy of the onsite guide and the big red book :)

I have both of the books, what i was checking was that it's OK to run a spur from an FCU that is supplying fixed equipment, looking at the BRB (appendix 15) it would be OK if the FCU is on the ring main (as the previous poster pointed out) but not if its spurred off. I will investigate and see how its set up.

Down2earth
 

Reply to spur from an fcu ok? in the Australia area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
784
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
759
I'm sure this has been asked before, but I just want to confirm: Currently I have a spur leaving a socket in the bedroom, into a 13A Switched...
Replies
3
Views
2K
Hi all, My mother wants a double socket adding next to a desk, behind the desk there is a 10mm (i dont know the MCB in the Consumer Unit) which...
Replies
4
Views
1K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
912

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock