Discuss Student BS60898 Type B trip question in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Hello

I'm a Level 2 electrical installations student and I have a question about Type B BS60898 circuit breakers.

I've been revising tonight and have noticed that the trip time on these is 3 to 5 times the rated current. What does this mean?

Say I had a 32A Type B would it trip over any current over 32A or would it trip at 32 x 3 = 96A as this is the three times the rated current?

Thanks

Jonathan
 
Hello

I'm a Level 2 electrical installations student and I have a question about Type B BS60898 circuit breakers.

I've been revising tonight and have noticed that the trip time on these is 3 to 5 times the rated current. What does this mean?

Say I had a 32A Type B would it trip over any current over 32A or would it trip at 32 x 3 = 96A as this is the three times the rated current?

Thanks

Jonathan

Yes you are correct. A 32A Type B miniature circuit breaker should not trip in less than 0.1 second and not more than 5 seconds with 3*In. A current equal to 5*In should trip the Mcb in less than 0.1 seconds.

Regards

Buckfast
 
it will trip, but not as quickly. e.g. it will take 200 secs. @ 60A to trip. the larger the current, the quicker it will trip.
 
Thanks to all!

So it trips quicker if the current is 3-5 times. One last question.

If I have a shower that is rated 8.5Kw Ib= 8500/230= 37A. How is a 32A type B suitable? Is it because the shower won't draw the full load? And if so, why won't it?

Thanks
 
MCB will stand a small overcurrent almost indefinitely.
 
Thanks to all!

So it trips quicker if the current is 3-5 times. One last question.

If I have a shower that is rated 8.5Kw Ib= 8500/230= 37A. How is a 32A type B suitable? Is it because the shower won't draw the full load? And if so, why won't it?

Thanks
I would say 32A Mcb not suitable. A 40A would be more appropriate. With regard trip times, The larger the overload/fault current the quicker the Mcb will trip
 
433.1 specifically precludes the example of using a 32A breaker for a 37A load: "Every circuit shall be designed so that a small overload of long duration is unlikely to occur."

More specifically. 433.1.1 (i): "The rated current or current setting of the protective device (In) is not less than the design current (Ib) of the circuit."

Looking at Fig 3A4 in the regs (p 325), looks like the 32A breaker might never trip at currents upto about 40A (ish, maybe a bit more). But the regs above say you shouldn't do this.
 

Reply to Student BS60898 Type B trip question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
764
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
659
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
914
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock