Stupid question but can you connect swa to flex cable via a 15/5amp terminal block in a waterproof terminal box?
Tom
Tom
Discuss Stupid question swa to flex via terminal block in the Australia area at ElectriciansForums.net
Yes.
for example, use one these...
25mm 2 Way Galvanised Conduit Box | *************
with appropriate glands for the SWA & flex
&
assuming the cables are the same csa.
also read this, substitute silly with stupid...
http://www.electriciansforums.net/e...l-forum/29586-silly-questions.html#post232904
Good forum this!
And use a ''cast lid'' with gasket, and brass screws, if being externally mounted, ....not the usual thin metal plate lid variety!!