Installing Swa 35MM 4 c,to new school block.
This supply will come of a MPB,nearby,to me the supply to this MPB does not comply.
Concern once again are the size of the bonding conductors realative to the the Main REC supply.
The drawing we have,have no input on this, it’s a Tncs system,& earth bonding will be required.
In a nut shell, even @ this moment the supply does not comply,in my opinion.
Any thoughts,on this,once again Swa being used as cpc & bonding conductor.
 
Best to write to the designer to highlight your concerns and ask for comments.

Also state that they will be designated as the "designer" on the EIC when you issue it.
 
  • Like
Reactions: Pete999
The 35mm is inadequate to support main protective bonding. The minimum size for 10mm bonding would be 50mm four core.
 
The 35mm is inadequate to support main protective bonding. The minimum size for 10mm bonding would be 50mm four core.
The main bonding cable would be installed separately, the issue is the MPB
Best to write to the designer to highlight your concerns and ask for comments.

Also state that they will be designated as the "designer" on the EIC when you issue it.
on the case tomorrow
 
Whoever designed the new cable probably did so from a drawing, not a site visit, so would be unaware of the actual existing.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Sub main & bonding conductors
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
cliffed,
Last reply from
snowhead,
Replies
4
Views
2,034

Advert