Recently had to install additional fuse board for extension.
Spilt tails at source, henley blocks and installed 100A switched fuse to supply new board which is located other side of house.
25mm tails are 10m long, done calc all ok, and checked with local DNO all ok.
Got the tails up the cavity through to the first floor joists along and down the cavity on other side, but still not sure if should change switched fuse to RCD. Thought switched fuse was the correct way ? And presumed you'd only need RCD if less than 50mm deep?
Any thoughts please?
Thank you,
Sy