Hi guys please bear with me as I am new to the electrical game


I have done a private job and run a garage board to a shed with a six mm amoured fone all relevant test on the curcuits
And done a zs at db but do I have to r1 r2 the sub mains to put on the test results or is tbis not needed and do I need to do
Ir test on sub mains and put it down on the certificate or just the radial xuircuit and lighting




Cheers guys
 
Yeah I have done 1 test cert and filled in but first two curcuits are on test sheet is incoming rcd 40 amp mains 61008 rcd the 6 mm mains to this board do I have to r1 r2 this and write on test sheet

Cheers guys sorry I am all new to this need some advice
And yes will notify as I know it comes under part p
 
Yes you carry out all tests on the submain, it is a new circuit so you test it as such.
You record the results on the first test results sheet in your certificate.
You record the test results for the circuits on the sub-board on your second test results sheet.

Alternatively you could record them all on the same sheet as long as you make a clear distinction between them.
 

Reply to sub mains help newbie in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
Looking for some guidance here. I'm currently shadowing a guy and we're testing a new extension on a school. 3 phase TNCS supply from the original...
Replies
6
Views
2K
Afternoon all. Bear with me on this one... Despite having been involved in the electrical industry for many years, I'm only just about to embark...
Replies
15
Views
2K
Hi, this is my first post here. I have a 3 phase board with a 40amp circuit breaker supplying a single phase board to a small office. I...
Replies
3
Views
3K
My father In law is selling his property and had a EICR done recently requested by the buyers. I thought the report was not the best quality with...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock