Hi all,

I am installing a Radial A2 circuit which by rule it should have an MCB of 32Amps, but when I reference the table 4D1A using reference method A or B, current are 26 and 32A respectivitly..

So the question is why we go for a 32A mcb and not 25A one?

Thanks
 
Proper circuit design should be applied to all circuits.

If you are looking in the OSG at standard radial circuits it is made clear in that section that the stated cable sizes are minimum sizes and that calculation is necessary to design the circuit properly.

I'd pretty much ignore the OSG if you are learning circuit design.
 
The OSG does have a couple of handy bits such as max lengths for circuits and conduit capacity for example. Also the max Zs with 80% and Cmin applied are quite handy for a quick reference.
True. It's all in the regs too though.
 
Hi all,

I am installing a Radial A2 circuit which by rule it should have an MCB of 32Amps, but when I reference the table 4D1A using reference method A or B, current are 26 and 32A respectivitly..

You need to go up a cable size if its CCC is 26A.

The cable size in the book is the minimum permitted for that standard circuit, not the only size you may use.

Also you should not be directly applying the CCC from the tables, these should be adjusted using the cable rating factors for your particular installation.
[automerge]1595961665[/automerge]
regs book is too expensive to take to site and get it dirty. :(

The apprentice will never learn if you're only hitting him with an OSG, you need the big book to really get your point across!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Suitable MCB for Radial Circuit?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
mark meli,
Last reply from
Dustydazzler,
Replies
6
Views
2,585

Advert