Hi all,

I am installing a Radial A2 circuit which by rule it should have an MCB of 32Amps, but when I reference the table 4D1A using reference method A or B, current are 26 and 32A respectivitly..

So the question is why we go for a 32A mcb and not 25A one?

Thanks
 
Proper circuit design should be applied to all circuits.

If you are looking in the OSG at standard radial circuits it is made clear in that section that the stated cable sizes are minimum sizes and that calculation is necessary to design the circuit properly.

I'd pretty much ignore the OSG if you are learning circuit design.
 
I'd pretty much ignore the OSG if you are learning circuit design.
The OSG does have a couple of handy bits such as max lengths for circuits and conduit capacity for example. Also the max Zs with 80% and Cmin applied are quite handy for a quick reference.
 
Hi all,

I am installing a Radial A2 circuit which by rule it should have an MCB of 32Amps, but when I reference the table 4D1A using reference method A or B, current are 26 and 32A respectivitly..

You need to go up a cable size if its CCC is 26A.

The cable size in the book is the minimum permitted for that standard circuit, not the only size you may use.

Also you should not be directly applying the CCC from the tables, these should be adjusted using the cable rating factors for your particular installation.
[automerge]1595961665[/automerge]
regs book is too expensive to take to site and get it dirty. :(

The apprentice will never learn if you're only hitting him with an OSG, you need the big book to really get your point across!
 

Reply to Suitable MCB for Radial Circuit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
965
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
812
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
737
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock