Discuss suplementary bonding again in the UK Electrical Forum area at ElectriciansForums.net
T
thekingiam
just trying to get my head around this as never tested before, bathroom pipes all circuits rcd protected no power except lights, connected one probe to landing cpc in socket and the other to sink pipe tested insulation resistance on 500 volts 1 meg ohm meter reading 0000.00 X underneath 1 volt checked continuity at 20 ohm and got 1.3 ohm.
am i doing this correctly and if so as it's not above 0.2 M ohm do i take it that i need suplementary bonding?
Measure between simultaneously accessible metal parts, such as radiators, taps, pipework and cpcs of circuits within the bathroom.
the values you are looking for are <0.05 ohms or >22k ohms
The formula for the latter is Rx > Uo/IAN -Rb, where Uo = 230V, IAN = 10mA, Rb = 1k ohm
Start with 701.415.2 then if there is still doubt then look at 415.2.2.
From your results in the OP, there is not enough IR to be isolated and too much resistance to be effective enough to keep the touch voltages to a minimum
If there is RCD protection, MPB and the bathroom lighting circuit complies with 41.1 then SBCs may still be required.
The chances of a fault caused from the lighting circuit is probably slight but there are other circuits in the property that may transfer a fault voltage onto the pipework in the bathroom location.
Not that it has ever happened on my watch.....
With supplementary bonding you are checking to see that the touch voltage between simultaneously touchable parts will not exceed 50v under fault conditions.
If all ccts are 30mA protected you are looking at 50/0.03 is 1667 ohms. Between all pipe work and the MET.
Above this but below 23k ohms will require supplementary bonding.
This formula proves 'effectively connected to the MET'
Obviously if you have a non Rcd cct you need to replace the 0.03 with the fault current required to operate the OCPD.
Hope this makes sense!!
It is based on the current not to be exceeded flowing through the body.
Taken as 10mA.
The formula is Uo/ 10mA - 1000
(1000 is the resistance of the body)
This can be ignored for these purposes.
So 230/.01 = 23000 or 23k ohms.
Some use 30mA but IMO 10mA is much much safer.
ok retested low ohm meter got 0.47 ohm so
0.47 x 50 / 0.03 = 783.33 well below 16670
so no sup bonding required, am i correct anyone?
No, it's not done like that.
The 0.47 must be less than or equal to 50 / 0.03 (1667) which obviously it is.
This is why as long as the conditions of 715.412 (iv),(v),(vi) are met then supplementary bonding is not required.
Also, above 23kΩ between part and MET is considered isolated and even main bonding is not required.
Reply to suplementary bonding again in the UK Electrical Forum area at ElectriciansForums.net
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Those week I have mostly been fitting 20 x 10W flood lights on the sloping edge of a converted mill ceiling, nothing is straight, nothing level...
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
4K
My brain has been exercised a bit by this. Am I on the right lines with this extremely simplified example: If we take: -TNCS installation with a...
4K
So having a look at the electricians guide to the building regulations, section 7 safe working. 7.3 is about pre work tests and is states that...