rattlehead85
Ok this has probably been covered before but still remains a grey area for a lot of sparks out there..
In a room containing a bath or shower reg 701.415.2 stipulates that local supplementary bonding shall be established connecting together the terminals of the protective conductor of each circuit supplying class I and class II equipment to the extraneous conductive parts of the location.
Now if conditions iv v and vi of 701.415.2 are not met do we A) provide additional supplementary bonding using green and yellow cable as described above.
or B) apply the equation of reg 415.2.2 first to determine if A) is needed.
Or is it that R<_ 50v/Ia is only supposed to be used to confirm the adequacy of existing bonding installed..
Tin hat at the ready[emoji21][emoji21][emoji21]
In a room containing a bath or shower reg 701.415.2 stipulates that local supplementary bonding shall be established connecting together the terminals of the protective conductor of each circuit supplying class I and class II equipment to the extraneous conductive parts of the location.
Now if conditions iv v and vi of 701.415.2 are not met do we A) provide additional supplementary bonding using green and yellow cable as described above.
or B) apply the equation of reg 415.2.2 first to determine if A) is needed.
Or is it that R<_ 50v/Ia is only supposed to be used to confirm the adequacy of existing bonding installed..