that's about as useful as a wet fart in a thunderstorm. what is "ground flash density" FFS.
how do you choose suitable surge diverter/arrester in au to protect single phase residential from surge/ lightning. ie ka rating ? 20ka/40/ka, ph to e
What is the earthing system of your electrical installation? is it from your electricity supplier or do you have an earth rod?
The biggest difference is between "Type 1" SPD that are rated for a direct hit (10us/350us pulse shape) and "Type 2" that are rated for induced surge (8us/20us pulse shape). While you will see similar peak currents mentioned in the 10kA to 40kA region, the order of magnitude difference in pulse duration means there is a massive difference in energy handling.
Generally if the building has lightning protection conductors you must use Type 1 (or combined Type 1+2), but also if you are at the end of a long overhead line and/or in a high region of activity you might be best to go for the high energy handling of them as well as they will last longer at medium surge energies.
Otherwise you use Type 2 as they are enough for nearby surges, and also at sub-boards that are 10m or more away from any main Type 1 incomer protection.
As for the different ratings, you get different degrees of lightning protection system rating (I, II, III and IV) that cover the probability of being hit, survivability, etc. Basically it comes down to risk management.
This PDF document covers more than you are likely to need to know:
https://www.erico.com/catalog/literature/E907W-WWEN.pdf
True thing.....
I won't mention the place by name but there's a BIG 'rooftop' swanky bar and eating venue in central London that I did a couple of years ago. I was off site for a couple of days, came back..... to discover that someone who knows more about 'art' than physics had decided to clad the main bits of all of this in 3mm pure copper sheet. The look on the site agents face when I asked who'd done the lightning strike risk assesment was priceless ?
It is a myth that a metal roof is more likely to attract a lightning strike.
Not sure I agree with you on that.... a metal roof in isolation, absolutely - agree. But a metal structure which is by necessity fully bonded to earth......
a keen golfer was playing a round of golf with the local priest. , on the first tee, he missed the ball completely and swore "Bollox missed the -------". the priest tutted but said nothing.
2 hole later, same again "Bolloxmissed the -------.". Cutting a long story short, after the 5th occasion, the priest had had enough and said " if you swear like that again, God will strike you down".
on the 9th, similar missed hit and again " Bollox, missed the -------"
Suddenly, there's the sound of thunder in the sky and a bolt of lightning shoots down and stikes the priest stone dead.
a deep voice sounds from above.....
Reply to surge/lightning protection in the UK Electrical Forum area at ElectriciansForums.net
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Following the tragic tale from @telectrix about lightning damage to phones and modem leading to a serious loss of beer money I decided to take a...
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Evening all, Pretty straightforward I think. I was led to believe that surge protection needs to be fitted on all additions and alterations...
4K