An internal swimming pool (recessed into the concrete floor of a basement in a domestic house)

The pool has a metal frame

However all pipes feeding the pool are plastic

Am i right in thinking I do not need to bond the metal frame as it is not a extraneous metal part ?
nor do I need to TT the single phase circuit supplying the 6kw heater ?

It is a 4mm SWA protected by a 32a 30ma RCD
 
The pool, even though indoors, is in contact with the Earth via concrete so it is "extraneous" and needs bonding to construction rebar / metalwork, etc, or possibly even an earth mat (if TN-C-S supply, see blow to check regs). You may well see resistances to earth well under 100 ohm via damp concrete which is quite enough to cause open-PEN grief.

While you are unlikely to really see serious fault currents, check the minimum bod size as on TN-C-S it is going to be at least 10mm, and if it is related to the 200A plan in another thread, check the table for the values there.

Also look over the special area rules for swimming pools, not something I know the details of (beyond the fact it is in the regs and a very clear risk of shock).

I personally would go down the bonding route than even considering TT-ing it internally as too much risk of other circuit's CPCs being close.
 
The pool, even though indoors, is in contact with the Earth via concrete so it is "extraneous" and needs bonding to construction rebar / metalwork, etc, or possibly even an earth mat (if TN-C-S supply, see blow to check regs). You may well see resistances to earth well under 100 ohm via damp concrete which is quite enough to cause open-PEN grief.

While you are unlikely to really see serious fault currents, check the minimum bod size as on TN-C-S it is going to be at least 10mm, and if it is related to the 200A plan in another thread, check the table for the values there.

Also look over the special area rules for swimming pools, not something I know the details of (beyond the fact it is in the regs and a very clear risk of shock).

I personally would go down the bonding route than even considering TT-ing it internally as too much risk of other circuit's CPCs being close.
bond it back to the DB or just link all metal parts together?
 

Reply to Swimming Pool- bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Just had my design project handed back to me from my last block and I got everything right apart from one question Q9 I would take a photo but...
Replies
3
Views
1K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
566
I incorrectly posted this on the "electrician's forum" and got a bit of a cold shoulder. Looking for some tips on supplying my pool equipment...
Replies
4
Views
892

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock