Woodstore

I have just bought a small house in Portugal and with it a small swimming pool ( no metal steps just tiled steps). 2x 12 ac 300w lights are fitted with thick cables to a pump house/brick shed about 4m distant. Cables enter the pump house unconnected to anything. So need a consumer unit installed for the pump, 2 pool lights and a few sockets. The pump house is fed from the main house 18m away via 3 phase plus N cable feeding just the pump and pump house lights at the mo.
At the pool house, plan to add a 3 phase breaker and to balance it, each 300w transformer connected to different phase, 1 RCD for each pool light with its own overload breaker and 1 breaker for pump/lights/socket. To ask the right questions at the pool shop and get the right electrician, some help pls:
1. Is the 12v output of each transformer connected to its own RDC and overload breaker that then connects directly to each pool light?
2. Should the transformer primary be protected too?
3. The overload breakers for the pool lights, what size overload? Would guess 10A but as this is 12v (and not the usual 220v supply) and high current of 25A, what should the breaker rating be?
4. Is a local ground connection at the pool house consumer unit required given RCD breaker is to be used? Or is the neutral from the main house sufficient?
5. Does the pool/water itself need a ground connection? If so what's involved to retrofit it?


Many thanks
 
300watts@ 12V is, as you say, 25A, but the primary current @220v will be only 1.4A approx, but allow for the start-up surge of the transformer. only the 220V part/s of the circuit/s need RCD protection. that's by UK regs. not sure if portugal is different.
 

Reply to Swimming pool lights in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
863
I need advice regarding an electronic problem on my Hayward Power-flo Matrix pool pump. I notice that : 1. Neutral wire from source has become...
Replies
4
Views
2K
I have an inground pool with a 22 year old, 120vac light fixture in a niche connected to water-holding conduit running to a switch in an...
Replies
7
Views
810
Installing a small above ground pool with a 1/2HP 120v pool pump. The house is older and has no grounding system that I can tell. Outlets are...
Replies
3
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock