Hi all.

When testing a lighting circuit fused down off the ring do I put it down on the test sheet as a separate circuit or mark it on the sheet that it's a spur?

Thanks.
 
I've also wondered about that because it's a bit like having another DB.

A B32 MCB on a ring would require a max Zs of 1.44 ohms where as a BS1362 13A fuse in an FCU would require a max Zs of 2.42 ohms for 0.4 sec disconnection.

Maybe it should have it's own test result sheet?
 
I asked a Part P assessor about this and he said that he would record the Zs for the ring on the test result sheet, as normal, and then note the Zs for the fused spur in the remarks
 
well, he would as he's getting paid for being pedantic rather than having to get the job done.
 
What would you do then? (assuming that Zs on the fused spur is a fair amount larger than Zs on the ring, otherwise it's not worth worrying about).

Think I might called it a separate DB and fill out a separate Sched Of Tests. If it's really a fullish lighting circuit in its own right, Only takes five minutes to fill out a one-liner Sched Of Tests.
 
I asked a Part P assessor about this and he said that he would record the Zs for the ring on the test result sheet, as normal, and then note the Zs for the fused spur in the remarks

Not keen. Zs recorded in the box should be the max Zs for the circuit regardless, IMHO.

Indeed I think that would probably be a good way to fail your 2391/2/4/5. Are you allowed to fail your assessor? ;-)
 
Last edited by a moderator:
agreed. Zs should be read from the furthest point of the lighting spur. then if it's above the 1.44 for a 32A MCB, an explanatory note on the cert. mentioning the 5A 1362 fuse at origin of spur.
 
agreed. Zs should be read from the furthest point of the lighting spur. then if it's above the 1.44 for a 32A MCB, an explanatory note on the cert. mentioning the 5A 1362 fuse at origin of spur.

Nice one Centurion, like it, like it.

I wonder if NICEIC, ELECSA, NAPIT etc. all run around yelling SPLITTERS!!!!!! at each other?

<scene: the IEE, Savoy Place>
"We're NAPIT"
"We're ELECSA"
"We've come kidnap the President of the IEE, issue demands"
"So have we"
"We thought of it before you!"
etc.
 
agreed. Zs should be read from the furthest point of the lighting spur. then if it's above the 1.44 for a 32A MCB, an explanatory note on the cert. mentioning the 5A 1362 fuse at origin of spur.

And including the max Zs for the ring, I think, to show that disconnection times are met on the ring as well :)
 

Reply to Testing a lighting circuit fused down off the ring in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
643
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
837
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock