Hello everyone!
Has anyone been asked to test the main building incomers like ACBs as part of Periodic Inspection? If yes, do you give this part of the work to 3rd party? and what is the process and how you verify the report?
some of my bigger clients are asking for this test to be done.
Thanks in advance
 
it would be best to clarify what the client means by testing.

ACBs should be racked out and various internal checks done periodically. Also at least once a year ACBs should be switched to exercise the springs. If there is a PLC this should also be confirmed as operational and all batteries and chargers conformed as in good order.

I would not entertain using any one other than a competent person to rack out an ACB and carry out the internal testing.

The switching and testing the PLC is something we do internally annually but we do have a level of competence to do this and a sound knowledge of the system it is not the competence required to rack out and test internally an ACB.
 
it would be best to clarify what the client means by testing.

ACBs should be racked out and various internal checks done periodically. Also at least once a year ACBs should be switched to exercise the springs. If there is a PLC this should also be confirmed as operational and all batteries and chargers conformed as in good order.

I would not entertain using any one other than a competent person to rack out an ACB and carry out the internal testing.

The switching and testing the PLC is something we do internally annually but we do have a level of competence to do this and a sound knowledge of the system it is not the competence required to rack out and test internally an ACB.
I guess they want to make sure the springs would work properly and disconnects the load if they want to manually switch it off . also in case of a fault, it trips safely. which if I am not wrong, means all the procedure that you have mentioned shall be done and it is better to be done by a specialized company not part of general fixed wiring tests
 
The ones I've seen tested were;

Mainly 2000amp, but size won't have too much effect on the costs.
Tested by a specialist
Required isolation of the (11kv) incomer by the DNO
Consisted of inspection / torque check of terminations.
Verification of settings to suit site
General condition check
Simulated load test using a test rig and a built in test facility.

Replacement with spare if faulty or failed test.

This was a new program set up after a series of ACB failures.
The failure wasn't to trip it was failure to reset due to springs / levers jamming in the open position.

As per ESSEX, they should be operated routinely.
 
The ones I've seen tested were;

Mainly 2000amp, but size won't have too much effect on the costs.
Tested by a specialist
Required isolation of the (11kv) incomer by the DNO
Consisted of inspection / torque check of terminations.
Verification of settings to suit site
General condition check
Simulated load test using a test rig and a built in test facility.

Replacement with spare if faulty or failed test.

This was a new program set up after a series of ACB failures.
The failure wasn't to trip it was failure to reset due to springs / levers jamming in the open position.

As per ESSEX, they should be operated routinely.

Hi Snowhead Why did the HV need isolating to test the ACB ?
 
I guess they want to make sure the springs would work properly and disconnects the load if they want to manually switch it off . also in case of a fault, it trips safely. which if I am not wrong, means all the procedure that you have mentioned shall be done and it is better to be done by a specialized company not part of general fixed wiring tests
They also probably put a full load on it to make sure it trips
 

Reply to Testing ACBs during Periodic inspection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi Guys, looking at doing Initial and Periodic inspecting and testing. Looking between the CandG and EAL Just wondering if I can ask peoples...
Replies
16
Views
631
Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
341
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
924
Experienced Electrician, C&G 236 Parts 1 & 2, AM 1 & 2 18th Edition Am 2. (JIB Gold Card) I've been out of the trade for some time, but did a...
Replies
2
Views
835
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
469

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock