Hi I just installed a 5000va transformer 240 - 110 v and cant see what protection there is on secondary side for short circuit.

now i take it that it's a centre tapped safety isolating transformer because in getting half the secondary outlet voltage between line to earth (would it be visual if it was centre tapped via earth as i cant see earth going to coils at all )

now the question is do i need to install a double pole isolator on secondary side or would the mcb on primary side protect on a fault current on secondary side
i just had niceic out and he said that i need to join earth to neutral on secondary side of transformer i cant see how this would help and i think i would only get 55 v outlet total

the other problem is the Usa don't have fuses in there plugs so if the secondary side of transformer is fused at 40A then the flexes and equipment which are plugged in are not protected so has any one got a better idea other than putting 13A spurs in supplying each 110V socket

hope you can make sense of the way i put my questions etc

redface
 
If it's centre tapped then connecting neutral to earth will short half the windings out! The socket outlets should be protected by DP MCB's
 

Reply to transformers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Hey so I need help understanding this question and understanding it in the NEC.The service to a multistory building is 277/480-volt, 3-phase...
Replies
4
Views
2K
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K
Hi all, No electronic knowledge here. The plug/transformer of a led lightstring is fried. Now I am trying to find a replacement on Aliexpress...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock