Evening. Did a Zs test today on a TT lighting circuit and got a reading of 335ohms. I haven't checked Ze yet but I'm presuming that's also in the same ball park. I'm aware of the upper limit Zs of 1667 and the advice contained within the good book that states Zs should be below 200, so I'm in the middle. I've advised homeowner that it should be reduced if possible and I see a couple of options; Add an earth rod or increase the main earth with a 16mm CSA cable (it's currently only 6mm). It's been pouring with rain all week so no point adding water. Any other suggestions? Thanks
 
Changing the CSA of the cable to the stake isn't going to help that much with a RA that high... best add a 2nd and possibly a 3rd rod, and make sure they go nice and deep!
 
  • Like
Reactions: DPG and hightower
Changing the CSA of the cable to the stake isn't going to help that much with a RA that high... best add a 2nd and possibly a 3rd rod, and make sure they go nice and deep!
Where do we stand regarding the 200ohm limit though? If max is 1667 then why worry at all?
 
It is considered unstable above 200ohms
 
Changing the cable from 6 to 16mm will only make a tiny difference, less than 1 ohm for sure.
Although the high Ze is strictly speaking acceptable combined with 30ma RCD protection I'd try and get it lower.
A decent 5/8 rod even 2 coupled together should make a difference although I know how hard it can be to get a rod in the ground in many places 'down west' in Cornwall. :)
 
  • Like
Reactions: DPG
Yes
It is considered unstable above 200ohms
Yes, I got that bit as its stated in 7671 but can someone elaborate on the 'unstable' bit. What does that actually mean? Why should we worry as the max permitted is much higher? Trying to comprehend it (still). Cheers
 
Changing the cable from 6 to 16mm will only make a tiny difference, less than 1 ohm for sure.
Although the high Ze is strictly speaking acceptable combined with 30ma RCD protection I'd try and get it lower.
A decent 5/8 rod even 2 coupled together should make a difference although I know how hard it can be to get a rod in the ground in many places 'down west' in Cornwall. :)
It's on an estate so may be doable
 
The max 1667 ohms applies if the breaker controlling the circuit is 30mA. I would suggest a ze test carried out and a reading of sub <200 ohms should be obtained for a stable earth reading.
 
If it is on an estate probably isn't using the rod as a return anyway. Be interesting to know the Ze with the bonds isolated, could be a case of the earthing conductor doing no more than earthing the electrode.
 
If it is on an estate probably isn't using the rod as a return anyway. Be interesting to know the Ze with the bonds isolated, could be a case of the earthing conductor doing no more than earthing the electrode.
When I say estate, I mean that in the loosest possible terms!! There's a few houses, big for these parts!!. Ze (or Ra on a TT) is the next move and then perhaps an extra rod. May call dno too to enquire. Thanks very much.
 
The max 1667 ohms applies if the breaker controlling the circuit is 30mA. I would suggest a ze test carried out and a reading of sub <200 ohms should be obtained for a stable earth reading.
All circuits are protected by a front end 30mA RCD so happy with that.
 
  • Like
Reactions: Davisonp
Yes

Yes, I got that bit as its stated in 7671 but can someone elaborate on the 'unstable' bit. What does that actually mean? Why should we worry as the max permitted is much higher? Trying to comprehend it (still). Cheers

The fact is that Bs7671 does not give a maximum Ra value and does not state that the value must be stable....only that a value exceeding 200 ohms may be unstable. Nobody has ever given a valid reason as to why it needs to be stable as far as I can recall.
People pluck values out of the air for their preferred maximum..The NIC seem to favour 100ohms,and I recall a poster on here saying he gets twitchy if it's over 80 ohms. Nobody has ever given a valid reason for their preferred value.
If your Ra is around 335ohms then it is in full compliance with Bs7671 and you need do no more, although you may choose to .
In that case pluck a figure out of the air like everyone else seems to do.
 
Mind you 335 at the moment when it's rained heavily for ages and the ground is pretty saturated could go sky high when the ground dries out.
 
Mind you 335 at the moment when it's rained heavily for ages and the ground is pretty saturated could go sky high when the ground dries out.

Probably not by around 1300 ohms though!
This is where it gets silly because of 7671's vague requirements, it's left to the tester/installer to decide what is acceptable...10...20...80...100...200 ohms? Whatever you fancy.
 
  • Like
Reactions: Dave OCD
Mind you 335 at the moment when it's rained heavily for ages and the ground is pretty saturated could go sky high when the ground dries out.
Yes - my thinking too. I haven't checked the 'above 200 unstable' statement in Table 41.5 but I'm prepared to accept it.

For a really good debate - what code would you give this, if any? :)
 
  • Like
Reactions: Dave OCD
I've read here, that depending on how you carry out your Zs test, you might not be getting an accurate figure. Try bypassing RCD and two wire high current test. See what result you get then? Do Ze test, R1+R2 test?
 
The fact is that Bs7671 does not give a maximum Ra value and does not state that the value must be stable....only that a value exceeding 200 ohms may be unstable. Nobody has ever given a valid reason as to why it needs to be stable as far as I can recall.
People pluck values out of the air for their preferred maximum..The NIC seem to favour 100ohms,and I recall a poster on here saying he gets twitchy if it's over 80 ohms. Nobody has ever given a valid reason for their preferred value.
If your Ra is around 335ohms then it is in full compliance with Bs7671 and you need do no more, although you may choose to .
In that case pluck a figure out of the air like everyone else seems to do.
Ha ha! That seems to sum it up nicely Wirepuller! I'll have to discuss with the customer and see what she wants to do but an extra earth rod is looking likely. Cheers
 
Yes

Yes, I got that bit as its stated in 7671 but can someone elaborate on the 'unstable' bit. What does that actually mean? Why should we worry as the max permitted is much higher? Trying to comprehend it (still). Cheers

BS7671 only states that values above 200 ohms may be unstable, it is not a definitive figure or a target value.
You should aim to achieve a value of Ra as low as possible, ideally low enough for ADS.
Instability is often a result of seasonal changes in ground conditions, especially cold weather causing freezing of the ground. A number of deep driven earth electrodes in parallel will provide a far more stable value than a skinny 4' rod.
I usually start with 2x 8' long 5/8" dia rods spaced as far apart as possible for a small installation and take it from there.

If soil conditions prevent driving the rods to a sensible depth then other options need to be explored such as horizontal electrodes.
 
  • Like
Reactions: Davisonp
When I say estate, I mean that in the loosest possible terms!! There's a few houses, big for these parts!!. Ze (or Ra on a TT) is the next move and then perhaps an extra rod. May call dno too to enquire. Thanks very much.

Ze and Ra are not the same thing.
 
  • Like
Reactions: Davisonp
The fact is that Bs7671 does not give a maximum Ra value and does not state that the value must be stable....only that a value exceeding 200 ohms may be unstable. Nobody has ever given a valid reason as to why it needs to be stable as far as I can recall.
People pluck values out of the air for their preferred maximum..The NIC seem to favour 100ohms,and I recall a poster on here saying he gets twitchy if it's over 80 ohms. Nobody has ever given a valid reason for their preferred value.
If your Ra is around 335ohms then it is in full compliance with Bs7671 and you need do no more, although you may choose to .
In that case pluck a figure out of the air like everyone else seems to do.

It needs to be stable as an unstable value will change and could exceed the maximum permitted value with seasonal variations in ground conditions.

Stability is not just about getting a low Ra, a high Ra from a well designed earth electrode will be more stable than a low Ra from a single short rod.
 
  • Like
Reactions: DPG and Davisonp
Ze and Ra are not the same thing.
True, but unless the Ra is very low, there's little practical difference.

Really, the figure that matters for ADS is the full earth fault loop impedance, of which Ra is just a part.
 
It needs to be stable as an unstable value will change and could exceed the maximum permitted value with seasonal variations in ground conditions.

Stability is not just about getting a low Ra, a high Ra from a well designed earth electrode will be more stable than a low Ra from a single short rod.

Good reason for stability, (perhaps)!.....but the 'over 200 ohms may be unstable' guidance is clearly a joke as stability has nothing to do with the ohms value of the electrode. The OP's 335ohms may well be more stable than another rod with a 50ohm value.
 
I've read here, that depending on how you carry out your Zs test, you might not be getting an accurate figure. Try bypassing RCD and two wire high current test. See what result you get then? Do Ze test, R1+R2 test?
The OP hasn't actually tested the earth rod or got a Ze figure yet.

So perhaps we should wait for that before we start hammering in new earth rods etc ;)
 
  • Like
Reactions: David M
I had an argument with a NIEIC assessor over this very subject. During an assessment a good few years back one of the installations was a TT.
The Ze measured at the time was 107 ohms, the assessor questioned this value.

I responded by stating that in the regs a value of less than 200 ohms was considered stable and acceptable. He refused this and said that the NICEIC would not accept a value greater than 100 ohms.

I was unaware of this at the time and asked for a valid explanation for the reasoning behind this? He had no definitive answer and just kept repeating that it was just not acceptable by the NICEIC. I argued that it was by the regs guidelines and therefore was no problem. Anyhow he got the hump and failed my assessment based on the fact that I had not complied with the NICEIC standards. I phoned the NICEIC office explained what had transpired and complained about my failed assessment. They couldn't explain to me why the value of 100 ohms was the acceptable one set by them. They just quashed the failure and re-instated my compliance with no other action or assessment required.
 
Yes - my thinking too. I haven't checked the 'above 200 unstable' statement in Table 41.5 but I'm prepared to accept it.

For a really good debate - what code would you give this, if any? :)

I'd seriously consider a C3 if part of an EICR or maybe no code and a comment, I do like to see a value well under 200 ohms ideally.
 
If the ze test on the electrode was >200 ohms i wouldnt hesitate to c3 it.
 
Do you need to?

My understanding of C3 is that the item does not comply with Bs7671 but is not considered to compromise the safety of the install. So a C3 cannot be applied if it complies with Bs7671.
Some might argue that as 200ohms is mentioned then that is effectively a regulation, however a maximum Zs of 1667 ohms would seem to contradict that.
TBH though it's a bit academic either way....a C3 will not stop a satisfactory EICR so it hardly matters really.
 
I meant do you need to note a Reg number.
 
  • Like
Reactions: wirepuller
What regulation would you document for the customer when you c3!

Bs7671 states ver 200 ohm of main electrode would be a unstable earth reading, zs & ze are diferent things. Zs being max value of a final circuit
 
We still haven't had the Ze reading yet, have we?
 
NoZe we haven't.
 
  • Like
Reactions: Hellmooth
542.2.4
The type and depth of an earth electrode shall be such that soil drying and freezing will not increase its resistance above the required value

Just food for thought,if everybody were to comply with the above regulation,the questions about stability would not be relevant :)

Now,If the value were low enough to operate the Rcd (be it a 30,100,300 or 500) and that value was typical of the conditions found in the area, the Ra could be almost any figure below the operating value as long as it does indeed operate the device

My conclusion would be the maximum resistance of the earth electrode can be almost anything you want it to be, as long as the above reg is satisfied,the 100 ohms or 200 ohms or even higher may be figures that may be of little practical benefit :clapping:
 
542.2.4
The type and depth of an earth electrode shall be such that soil drying and freezing will not increase its resistance above the required value

Just food for thought,if everybody were to comply with the above regulation,the questions about stability would not be relevant :)

Now,If the value were low enough to operate the Rcd (be it a 30,100,300 or 500) and that value was typical of the conditions found in the area, the Ra could be almost any figure below the operating value as long as it does indeed operate the device

My conclusion would be the maximum resistance of the earth electrode can be almost anything you want it to be, as long as the above reg is satisfied,the 100 ohms or 200 ohms or even higher may be figures that may be of little practical benefit :clapping:

Good points....I wonder how compliance with that regulation could be verified on an EICR? It would be very difficult to gauge the depth of an electrode without digging it up!
 
  • Like
Reactions: Des 56

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
TT High Zs
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
42

Advert

Thread statistics

Created
paulk11,
Last reply from
David M,
Replies
42
Views
5,348

Advert