Hello.
When inserting two or three conductors in a screw terminal (in a socket) is it best practice to twist the ends together or not to do so?
 
Thanks very much. I can see pros and cons each way. Is there one factor which dominates?

Are you talking stranded wires? Or standard T&E? And into what - the back of a 13A socket?
 
do not twist.

in my humble opinion.
 
  • Like
Reactions: DPG
terminals in fittings are designed to accommodate a certain amount of conductors.
i have never seen a manufacturers instruction for terminating that includes a recommendation to twist conductors together.
 
For 2.5 mm2 T&E, strip twice the amount of sheath off the wires than the depth of the terminal, then bend the end over with pliers.
Assuming two cables to the socket (RFC or daisy chained spur), place both folded over wire ends into the terminal, with the folded over end of the wires against the screw. When you screw down into the wire, some damage will occur, but this will be on the bits nearer the end, protecting the other half of the wire from damage.
The main problem with twisted wires is that if they are untwisted in any way, they become loose.
 
Compelling arguments. Thank you. The recommendation to fold over the end of the wire seems sensible to me
 

Reply to Twisted conductors in screw terminals in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt...
Replies
27
Views
1K
A rose in my 1970s kitchen ceiling became loose (one fixing screw had been inserted right on the edge of the hole in the ceiling) and when I...
Replies
3
Views
778
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
799
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
866
We have had RG11 installed in some flats for use with Virgin/Internet. It should I think have been RG6 but the guy at Virgin was insistent it...
Replies
4
Views
381

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock