What is the regs on terminating unused cable or even cores of an SWA cable. I know sometimes we can’t remove the cable completely sometimes due to being impractical.
Unused cores in a cable which has live conductors in it, or unused singles in trunking/conduit which has live conductors in it, should ideally always be connected to earth. This will prevent capacitively coupled (phantom/ghost voltages) or induced voltages appearing on the conductors.
Unused cable all together?
[automerge]1591968359[/automerge]
Unused cable all together? So you would ideally Earth all the cores to earth?
I'm not aware of any regulation that requires unused cores to be connected to earth.
Most control panels will have multi core cables coming in/going out where not all cores will be used, they are not connected to earth but labelled and terminiated correctly into din rail terminal blocks.
Does EAWR regulation 8 cover it ?
Precautions shall be taken, either by earthing or by other suitable means, to prevent danger arising when any conductor (other than a circuit conductor) which may reasonably foreseeably become charged as a result of either the use of a system, or a fault in a system, becomes so charged; and, for the purposes of ensuring compliance with this regulation, a conductor shall be regarded as earthed when it is connected to the general mass of earth by conductors of sufficient strength and current-carrying capability to discharge electrical energy to earth.
You can also have CT and VT wiring which are not classified as ELV.
I find it varies from industry to industry, Perochem usually insist on terminating and earthing. most industries try to at least terminate. In the ESI where I do most of my work there is often just no room to terminate so they are often labelled and left in the trunking sometimes there is a separate trunking just for parking spare cores.
Sometime but not always, it’s also 110V signals, motors and other LV equipment. For example a seven core cable but no thermistor or seal leak on the motor.
In which case they should be terminated to earth to achieve compliance with the EAWR as referenced earlier in the thread.
The fact that this is often not done does not indicate that it is correct not to do it, it indicates that a lot of people perhaps don't understand what should be done or why.
How is a core in a cable designed to be charged dangerous if it is becomes charged? Buy being terminated and labelled correctly it can not be mistaken by a competent person (non competent persons should not be entering a MCC or any other electrical equipment without a PTW). If a fault arises it is no more likely to cause danger than if all the cores are used.
While we're on the subject:
Socapex plug spider.
Reply to Unused SWA in the UK Electrical Forum area at ElectriciansForums.net
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...