Has anybody had to use the SMA grid code unlock system?
Looking at the SB4000TL once the code has been entered say via sunny explorer, is it possible then to simply use the grid setting dials (A & B) on the inverter or does it have to be changed using sunny explorer.
 
Yes Sorry, it was a bit vague. The inverter was comissioned with the switches set at A=0 B=1 so factory defaults and need changing to A=5 B=8 for G38 but it is displaying the message "Mod Grid Code Not Pos" so need the unlock code to make the changes. SMA are processing the unlock code request. The unlock code will be entered using sunny explorer. My question is once the unlock code is entered and accepted by the inverter is it OK to then exit sunny explorer and simply set the switches to A=5 B=8 or does the G38 grid settings have to be done via sunny explorer?

Hope that explains it a bit better

Thanks
John
 
You can't change the settings once the inverter has been up and running for 10 hours. We found that out the hard way!
Pretty sure you need a bluetooth enabled laptop to be able to enter the code and if memory serves it then enables you to access a different menu and change the grid connection info.

hope this helps
 
Thanks for all your input, as it turned out I didn't really need the unlock code just needed to look at the actual problem and read the warning messages properly. There was the first message "Mod Grid Code Not Pos" but then followed by another message ensure DC supply. Having re-seated the solar switch it all fired up correctly and accepted the G38/1 settings. It tages SMA 24-48 hours to process the unlock code request, so who knows it might prove useful in the future.

I should have listened to Corporal Jones from dads army "Don't Panic Captain Mainwaring"

Thanks again.
John
 

Reply to Using SMA Grid unlock codes in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hi, Really just for info. not a problem or anything. (to be honest also wanting to be sure it is taking from solar as much as possible & can you...
Replies
2
Views
1K
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
Hello ! I am building for some time a cct to drive a 3digit multiplexed LCD. (from aliexpress) From the sellers on aliexpress I managed to find...
Replies
7
Views
1K
I have a client on a Superdeal tariff from SSE, the Superdeal Meter has 3 sets of tails coming out of it feeding 3 DBs: (i) DB1 - the main board...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock