Would entering each RCD as a line on the schedule of test results be correct? If so, what would be entered in boxes such as Zs?
 
Use N/A for not applicable.

If I’ve got a split board, then top line is rcd1 with the rating, trip time etc.. then circuits 1,2,3,4,5 for example. Then another unnumbered line with rcd2, followed by circuits 6,7,8,9….

I find it pointless repeating the same trip times on 5 lines for each of the individual circuits
 
With dual RCD boards I just write the circuit numbers and details/test results then bracket them together on the right hand side as 'RCD1' and 'RCD2' .
 
Use N/A for not applicable.

If I’ve got a split board, then top line is rcd1 with the rating, trip time etc.. then circuits 1,2,3,4,5 for example. Then another unnumbered line with rcd2, followed by circuits 6,7,8,9….

I find it pointless repeating the same trip times on 5 lines for each of the individual circuits
Cheers, this is what I have done previously.
 
  • Like
Reactions: Dave OCD
Nothing is right or wrong provided it is clear.
 
Nothing is right or wrong provided it is clear.
I’ve not been on here for while hope you are all fine and well?

When recording the trip times I only record the x5 highest value (both sides of waveform) where the rcd is being used as additional protection. However if rcd is used as fault protection I then record the highest value at x1 (both sides of waveform) is this ok?

I don’t repeat this time for all circuits I normally put RCD 1 then list circuits below and then RCD 2 with circuits below that and record the above just on the RCD section.
 
I’ve not been on here for while hope you are all fine and well?

When recording the trip times I only record the x5 highest value (both sides of waveform) where the rcd is being used as additional protection. However if rcd is used as fault protection I then record the highest value at x1 (both sides of waveform) is this ok?

I don’t repeat this time for all circuits I normally put RCD 1 then list circuits below and then RCD 2 with circuits below that and record the above just on the RCD section.
Hello stranger. Just 1X for either additional or fault protection now. It changed with the new amendment.
 
  • Like
Reactions: Dave OCD
Hello stranger. Just 1X for either additional or fault protection now. It changed with the new amendment.
Good ok, on the software I use it doesn’t list x1 or x5 so that explains your answer and my question. Guess I need to do the new amendment 🫣 was waiting for the 19th 😂
 
  • Like
Reactions: Dave OCD

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
West Yorkshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
What’s the correct way to enter RCD’s on a split load board on a schedule of test results?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Ben1908,
Last reply from
Grant1987,
Replies
8
Views
4,783

Advert