When sizing cables and circuit breakers the much simplified rule is:

The cables maximum current carrying capacity must be greater than the current the connected equipment draws.
The fuse/circuit breaker used needs to have a higher current rating than the connected load, (so the fuse/mcb doesn't operate during normal conditions) but lower current rating than the cable used (so under fault conditions the circuit is switched off before the cable is thermally damaged. Remember, fuses and circuit breakers are mostly designed to protect the cables not the equipment connected to the electrical circuit

There are more factors to consider when selecting cable and circuit protection sizes and ratings such as:
The cables length.
How and where the cable is installed.
How many other cables your cable is bunched with.
The external earth loop impedance value.

Under 'fault conditions' a relatively small csa cable will survive a large fault current so long as the over current device disconnects the supply quickly
Even when everything is correctly sized and rated the conductors can still get surprisingly hot during heavy fault currents! Just not hot enough to cause damage to the cable.

JWs experiment is way more scientific than my attempt of just connecting bell wire across the mains:
 

Reply to When do amp ratings matter in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
852
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
958
I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
478
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
735
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
673

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock