Discuss Which value to record on EICR? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
newfutile
I work for a housing association where i have to conduct EICR‘s then conduct remedial repairs until a satisfactory report can be issued.
while inspecting bin store lights (fed by 1.5 3 core SWA) 1.56 was the ZS on initial inspection.
The swa outer was not earthed at either end.
now i have completed the repairs (earthed at both ends) the R1+R2 and ZS have obviously gone down.
i now get a ZS of 1.25 ohms.
which value should be recorded on the report?
Reply to Which value to record on EICR? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
I would appreciate some opinions on the following situation... I have been asked to comment on an EICR for a local community resource (church hall...