What's the requirement for wiring/containment above plasterboard ceilings within escape routes
Discuss Wiring in escape routes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I just done a load of flats in a old mill complex, the escape routes are all on cable tray mounted on the steelwork with all cables sat on top so will not fall in a fire unless it was with the building falling down itself.
Did you use any steel ties on the tray?
The generally accepted standard around commercial new builds these days appears to be steel ties every metre regardless of the fact the cables can't get off the tray.
In my view wiring would need to comply with 422.2.1 and 521.11.201, plasterboard will give up to a maximum of 30 minutes protection depending on specification and to what and how it is fixed. According to regs wiring systems need to be fixed with suitable fixings to non combustible fabric of building. The regs specifically state so not to hinder evacuation and firefighting activities. In my view this may well reasonably take place after the expected fire resistance of plasterboard.