Setup:
Consumer unit fed via sub main from a 60A fused isolator switch. This is connected to the service head MET via a 2m earth connection.

How would one go about both calculating and documenting the Zs?
Would you be treating the fused isolator switch as it’s own db and therefore be documenting Zdb1 (at point of isolator switch) and Zdb2 (at consumer unit). Zdb2 would be be the reading minus Zdb1? Or would you do Zdb1 and then the R1 + R2 of the sub main?

I’m getting myself confused so if anyone would be kind enough to talk through how you’d test this setup it would be hugely appreciated?
 
In this situation I record the distribution circuit and the switch fuse, as a DB with the one circuit, on is own test results sheet.

So you'd have;

1 = Ze - obvious.
2 = Zs at switch fuse.
3 = R1+R2 of distribution circuit.
4 = Zs at Db = 1+2+3.
 
Zs at 2 already includes [Ze + meter tails (R1+R2)] though - so 4 = 2+3
 
  • Like
Reactions: JosephandAmber
When you say distribution circuit are you referring to the sub-main?
 
When you say distribution circuit are you referring to the sub-main?
Is it a sub-main or is it just that the meter is >3m from the CU?
 
So we have meter, 3m run to fused isolator, 15m run to CU
 
So we have meter, 3m run to fused isolator, 15m run to CU
So it’s not a sub-main, it’s the consumers tails. In that case the 15m length of (hopefully) SWA is the distribution circuit in GBDamo’s post.

You can also measure the Ze at the CU the same way you would for a more traditional setup, but you need to remove everything other than the suppliers earth and the earth to the CU from the MET before you do.
 

Similar threads

D
Replies
5
Views
4K
UK Electrical Forum
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Zs for a CU with sub main and fused isolator
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
JosephandAmber,
Last reply from
dodger421,
Replies
7
Views
2,463

Advert