- Dec 18, 2011
- 5,379
- 6,731
- 405,788
- United Kingdom
With regards hot tubs, earthing always seems to be one of the most discussed points, especially with regards PME and extending the equipotential zone.
My question is why is TNS ok to extend and PME is 'questioned' (I wont say 'not allowed' as I believe it is, it just raises questions and many (not all
)electricians preferring to have a separate TT for the hot tub)?
I believe one problem is the possibility of potential between the PME earth (i.e supply neutral) and the local true earth, so client gets tingles when in contact with true earth and touching any exposed conductive part in hot tub earthed to PME (under normal conditions).
However, why is the above problem only with PME? Why would there not be a PD with TNS? With PME you have multiple earthing points, will they not be closer to the local true earth compared to the TNS system which connects to the neutral at the local source which will be further away?
I can see how under fault conditions (broken supply neutral) the TNS would still be ok compared to the PME but under normal conditions does this potential difference (between source earth and local earth) affect TNS as well as PME?
