Discuss Very old cut out info in the UK Electrical Forum area at ElectriciansForums.net
kropaske
Came across this recently. Looks like 30s, 40s maybe. Does anybody have any info, Bs number, kA values...
Is that the main incoming supply or in a flat?
What is it protecting?
Come on matey give us ALL the story...
Doesn't look isolated does it westy well spotted.
Looks like asbestos on the lid and that separator bar and no doubt the fuse holders. And it has seen some blow outs maybe thermal damage to live tail. The line on the right looks (exposed) and 10 mm away from the holders attached to the casing. Yeh I would get the DNO to look at that the neutral is fixed to the casing and the live can be accessed through that hole at the top. I think you are right it is 1930 as originally it looks as if it was fused on the neutral. So would not take much to short live to neutral if you dropped a screwdriver down there. Its downright dangerous.
This is in 1st floor and supply 2 flats on the 2nd floor.
There is another one on the ground floor but bigger with 4 fuses supplying ground and first floor.
So re supply to 2 flats, lets "assume" they are rewireable 3036 fuses, probably max 30A - so they are too small for the job (probably).
I think that this "fuse" is down to the flat owner - the bigger one downstairs is probably down to the supplier - where is the meter?
i Ze gave me open circuit but they said that this is not they problem. So i went
We will see i've put 32amp supply for induction hob and 16amp for steam oven + kitchen ring and i will be rushing there on Christmas Day so she can finish with the turkey...
Meter inside the flat...
I read that...I wonder if there is official info about replacing those cut outs.
I think i need to ask customer to approach them directly and get everything in writing. There is too much danger stuff going on there.
I guess it would be different story if this would have been a house - only 1 cut out to be change. Here is 6 in total so obviously shareholders would not be happy...
Please expand on this.......
Ze readings gave me infinity, Zs was good, all bonding in place. So flat was earthed through metal gas pipe. If you look at first photo there is metal conduit which takes tails to the flat but it was not connected to the enclosure therefore no earth to the flat. They did put earth clamp on this conduit and run 16mm earth to the MET inside property but forgot to do it on the other end. All flats are like this...
I did put link to get my Ze...
Silly question But:
That earth connection to the mains incoming, is that clamp just put over the paint, or has it been cleared for a good connection?
From the photo it looks like its just on top of paint.
:eek:Check the MOCOPA guide to see what it thinks about BS951 clamps attached to the incoming cable. As a matter of interest what was your Ze after you interfered err sorry interacted with the DNO equipment?;)
I have seen several of these but all are after the DNO/Meter. Used as fused isolators for control panels and such like.
On a separate note I contacted the DNO to get my cut out head upgraded from a 60 amp fuse with at best a 6mm (but more like 4mm) sweated on earth to a nice new 100amp with 10mm earth to MET. All because I was going to get two electric showers and an induction hob fitted, honest!
They did let slip that they had to up grade all 60A supplies is a reasonable request was made.
@kropaske they must change it by 2010 it says it in that guide I think. And for free. I am just amazed the DNO attended and left it like that, seriously negligent I would be having a head fit with them. In the nicest possible way!
I need to read this guide properly and get as many codes as possible and let customer to deal with them - all in writing rather then over the phone.
When i phoned 1st time about Ze and no earth they said "its not our problem" - i am kind of lost a bit as about a year ago i had same issue with Ze on another job. I' ve ask customer to rang them and they were there couple of hours later digging the concrete and repair cable.
When i phoned them 2nd time about cut out the guy said we will send someone to do "safety check".
When the dno guy came i've ask him to give me some report - he said "we dont do reports", so i have ask him is it safe - he said "i am not saying anything" - this is some kind of joke.
Is the neutral bar isolated from the enclosure.
Looks like it is, the neutral bar seems to be bolted through ebonite insulating bushes to those metal brackets.
The BS951 clamp on the incomer appears to have been fitted to the brass sweating thimble above the wiped joint. If this is the case, then it poses no danger to the cable and is probably the best way to make a remedial connection to the incomer. Obviously one should never put that type of clamp on the lead sheath itself because it can easily crush and short the cable.
Nice that it has METESCo (METropolitan Electric Supply Co) cast into the door. Save it if you can!
DNO came. Two young lads, quit rude, asked me at least 3 times why did i look in there for.
Anyway one brought 2 new Henley House Service Cut-out Holder with fuses and they start to look if it will fit.
Then phone rang and i went upstairs. 10 mins after i came downstairs they're gone! Never said nothing. But they did put new seal on the door!
As there was no power cut i assume they did not exchange those service holders.
Options are that:
1. They've somehow manage to fit 1631 in there but i doubt that spacing would be the same
2. They've put temporary seal and will come back tomorrow with different parts
3. They've put the seal and left it without any intention to come back.
I hope is not the 3rd one but we will see. I am very tempted to remove that seal and have a look
Contact the DNO again tomorrow, insist on speaking to the duty engineer and explain in precise and technical terms exactly what your problem is and what has happened so far.
Which DNO is this?
I can't make it out is there a hole in the butterfly nuts or is the gripple wire just wrapped around them in other words looking good,But doing nothing?
Think you are correct it doesn't "appear" to do anything.
Reply to Very old cut out info in the UK Electrical Forum area at ElectriciansForums.net
Hi All. Its been ages since I have been on here- Fortunately log in details stored on PC. I have just had a new boiler and 210 ltr unvented tank...
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
4K
Hello, we're looking at relocating the CU fairly urgently for a small business (retail shop) and came across this service head. Obviously need to...
4K
Hi guys, Whilst renewing my loft insulation I came across a few runs of very old cable. (Please see attached pictures). These cables are lead...
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...