They are type 4 Federal Electric devices and you need manufacturers data to compare Zs values. Sounds like you are out of your depth on this.
I’ve came across this type of DB before, and it had some newer mcbs fitted along the old ones, but they had to cut the lid of the DB to make them fit, unless they’ve put the wrong ones in and bodged it...

A3CA85F7-22DD-4F13-81F1-513579A3B30C.jpeg
 
717 or 721 are you not still in the same boat, or should I say caravan as the requirements regarding TN-C-S apply in both cases.
 
  • Like
Reactions: ruston
  • Creative
Reactions: ruston
upload_2018-1-20_16-19-8.png

made for the trailer trash ,got a tow bar ,has a house !
 
I have worked extensively in the static caravan park world. The only acceptable earthing arrangements for such buildings is TNS or TT.
TNCS can be used for supply upto external plastic meter box. Unit itself must be connected to earth rod and fed via 30mA RCD. I have also worked on units with SEB TNCS supplies housed in external meter cupboards. We never used the company earth and always fitted earth rods usually one was enough but quite often would fit 2 1 at each end of the concrete base and always tested the metal chassis and side walls to the earth connection.
 
  • Informative
Reactions: uksrevivor

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
TNCS PME on caravan site with static caravan EICR
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
32

Advert

Thread statistics

Created
fatgreeny09,
Last reply from
Sparkingmad,
Replies
32
Views
7,981

Advert