Ok all,

I'm looking at a shower install and need a bit of advice selecting the correct cable for the job.

The customer has a 10.5 KW shower. There are no cable factors to apply, all clipped direct in the loft from the consumer unit, above insulation, to the bathroom.

I was going to use 10mm T&E however the customer already has 25mm X 16mm mini trunking affixed from the ceiling, down to the shower.

It's not possible to top entry, only bottom entry is available, so the trunking runs down the side of the shower, with a 90 degree flat bend, bringing the route across the bottom.

The customer has refused for any damage to the wall tiles, it's a concrete wall too so can't drop through studs for rear entry.

I'm concerned that I can't meet the bend radius for t&e as it's a very sharp 90.

Has anyone and recommendations on a suitable flex that would fit the existing mini trunking?

Tenet
 
Hi Dave,

This was what I was thinking off hand. I know the H07 I have certainly won't.

The mini trunking is glued on with sticks like or something similar so thats gonna be fun.

Tenet
 
Ok all,

I'm looking at a shower install and need a bit of advice selecting the correct cable for the job.

The customer has a 10.5 KW shower. There are no cable factors to apply, all clipped direct in the loft from the consumer unit, above insulation, to the bathroom.

I was going to use 10mm T&E however the customer already has 25mm X 16mm mini trunking affixed from the ceiling, down to the shower.

It's not possible to top entry, only bottom entry is available, so the trunking runs down the side of the shower, with a 90 degree flat bend, bringing the route across the bottom.

The customer has refused for any damage to the wall tiles, it's a concrete wall too so can't drop through studs for rear entry.

I'm concerned that I can't meet the bend radius for t&e as it's a very sharp 90.

Has anyone and recommendations on a suitable flex that would fit the existing mini trunking?

Tenet
Can't get 10mm2 flex
 
don't personally recommend this, but i have seen 10mm where the sheath has been stripped off where it's inside the trunking. naughty but practical.
 
don't personally recommend this, but i have seen 10mm where the sheath has been stripped off where it's inside the trunking. naughty but practical.
Hi Telectrix,

The thought did cross my mind! It's within trunking which will be sealed but I have the mindset of "what's the next guy going to think". Though I doubt it will ever be open again!

Tenet
 
also, if you cut the assumed mitre off the trunking corner, then fit a manufactured corner, glued on, it will give you a tad extra room on the corner
 
  • Like
Reactions: TenetJohn

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cable Ideas
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
TenetJohn,
Last reply from
telectrix,
Replies
7
Views
1,404

Advert