I always find it odd when someone employs a fully qualified electrician and then questions everything they say.
Ordinary T&E may be rated at 70 degrees, but that's hotter than the maximum allowed from a domestic hot water tap. If I installed a cable in a domestic property that ran at anywhere near that temperature, I'd expect the customer to be on the 'phone pronto.
He didn't. The electrician refused to connect it up.
Personally I’d go with MI cos you can guarantee the one time it’s all on and trips will be Christmas Day and I don’t want you call me 😂
I was also thinking about Christmas Day - there's a country estate I look after that only has a 3 phase 100A supply for multiple dwellings, and Christmas Day is the reason that I as an electrician have been insisting on changing a few cookers to gas!
Be fair. The questions only started when a 2nd fully qualified electrician disagreed, and then what chance does Joe Public have of working out who is right? (I'd privately decided it was unlikely to be ok until it was established it is clipped direct.)
The cable running hot is one thing but how often are the terminations going to be checked for thermal creep and heat damage
I don't think it will get to that temperature in this case. Expected load is <28A, with the cable rated at 37A, it shouldn't get anywhere near that hot.
I tend to liken this to a commuter travelling a hundred miles each day to and fro for work. He can drive a fiat 500 or a nice two litre car. The strain on a 500 cc engine would wear the engine much faster than a 2l engine. Hence I would at least fit 6mm² cable for the longevity ensured.
All appears to be fine and the circuit safe to use, assuming the installing electrician is accurate with the details of the cable run, installation method, diversity and de-rating factors.
Me personally, though the diversity applied is fine, I always feel (and this is just my personal opinion not a professional judgement) that for cookers it can often seem a bit low. I understand and accept that maybe for general day to day use this would work perfectly fine. But still I would most likely either be a little more over cautious and go a size bigger than what calculates or ask the client what the likelihood of the cooker being used more than general is.
For example a good friend of mine's wife is an avid baker and spends many days in the kitchen baking, cooking probably much more than most normal households. In this scenario she would more than likely use much more than the applied diversity factor predicts.
At the end of the day Chris its your call, the circuit installed by all accounts calculates fine for intent and the installing electrician has provided evidence to suggest this.
Reactions: Chris C300
Hello all.
I'm the first guy.
I couldn't fit the oven not because I refused to but because I was on holiday.
Are those saying you need 6mm on a clipped direct no derating factor 32a circuit saying they disagree with the iet table? I'm not trying to be argumentative, I'm just following the book. Surely the iet have checked these as a long term load.
Cheers
Gc
Hello all.
I'm the first guy.
Cheers
Gc
First of all welcome! I hope the above doesn't make too painful reading - there are certainly gentler ways to join a forum!
There were some early responses before the fact it was clipped direct came to light. After that I think there was a consensus that it was compliant and you'd done nothing wrong(!).
It's true that a few of us (myself included) did express some surprise mainly because it's not something we encounter too often.
Hello all.
I'm the first guy.
Cheers
Gc
Welcome to the forum!
Can’t believe some here are advocating 10mm for domestic cookers. Absolutely no need unless it’s run through mountains of insulation making 6mm on a 32A OCPD non compliant.
Never known any domestic cooker to require more than 32A and I’ve had this argument many many many times before.
10mm for showers is another story. That I totally agree with.
Shower is a known fixed load (often less than initially expected if the rating of the shower is declared at 240V), and is not normally used for more than about 5 minutes at a time by normal people.
A cooker is an extremely and constantly varying load, for which we use a diversity formula to give the long term average maximum load. At times, the load will be well over that diversified current, and well above the rating of a 32A OCPD for hopefully short periods. For these reasons I would not use a 4mm cable for a cooker such as this.
At today's prices, the difference between 4mm2 and 6mm2 is 58p/m, so on a 15m run, would only have made a difference of less than £9 to the cost of the job.
The shower is a fixed load until a plumber changes it for a 10kW one!
Most have cable runs through insulation as they are invariably run through lofts. This is not so for cookers.
I’ve clamped many a cooker and even with a large range cooker it’s surprisingly difficult to get over about 30 amps.
When you clamp showers then it’s almost always around 40 amps with modern units.
A shower is nearly always run at full load whilst a cooker is usually well below its maximum rated current.
Having said the above I would’ve run 6mm probably, although 4mm sounds ok in this case. 10mm is overkill for domestic cookers though. Just not needed.
You give mountains of insulation as a reason but what about cables run in voids where the ambient temperature with heating pipes that can be at 60ºC+ is never really considered
There are a lot of appliances where the ratings are grossly over what they will run at in normal use, I suppose some of the debate in this thread revolves around a cable that may be close to it's limit and how any future changes in the building fabric may push it over that edge a cable clipped direct could be a cable that is boxed in a few months down the line
While the regs appear to address most of the new technologies it would appear that cooking appliances have been overlooked can we really apply the same diversity to an induction hob as we do to a ceramic or halogen hob when they are using totally different technologies, the induction hobs I have clamped seem very power hungry when compared to the older technologies
Since the first electric showers came to market at 6Kw the market has gone with bigger Kw's and even bigger Kw's is better and it is more likely you will find burnt cables and switches on shower circuits than cooker circuits
Reactions: nicebutdim
Hi, during kitchen refurbishment, the electrician installed a 4mm cable and 32a breaker for the new induction hob rangemaster oven that is rated at 16.2kw.
Same electrician couldn't connect hook up cooker, so I asked someone else to do it. The new electrician refused to connect up saying it needs a 10mm cable 45a breaker. Both professionals are in disagreement. Would be great to get a consensus here please. I want to use the oven without concern it may trip the breaker (5 induction hobs, 2 ovens and warming drawer)
It will be fine. Should of used 6mm really as best practice, but it's not unsafe if it's fused correctly which it is. Due to the installation method the cable rating may be slightly below 32 amps but as others have said with diversity applied to the cooker your unlikely to use over 32amps anyway. I mean 32amps for cooking is so much! An oven on full power will draw 13amps max but then it will switch off intermittently once up to temperature. Induction hobs do the same with intermittent pulses. You shouldn't have a problem. If the breaker starts nuisance tripping though then you shouldn't ignore this, but I doubt it will happen.
Except on modern cookers that use very poor quality terminal blocks! There is such a problem of them melting and catching fire (often on the factory side connections) the manufacturers, instead of going back to proper heavy duty type found in most cookers when I was fitting and repairing them as a job 16+ years ago, are now supplying metal covers that go over the same crappy plastic terminal blocks to contain the fire. Product manufacturers and designers are morons.
And now back to the other thread about AFDD's
  • Funny
Reactions: freddo
4mm cable, 32a breaker for 16.2kw Rangemaster installed by electrician
Chris C300,
davesparks,