Good Evening Folks!
I recently started on my house for an Outhouse/Summerhouse 35m away from main Property.
It requires :-
x5 Double Sockets
x2 Strip Lights
The sockets will be used for Televisions and Charging.
I have 2 ways i’d like to to this.
A 6mm SWA from Main CU/32A RCD clipped Direct to Outhouse.
Onto the back of a 2.5mm Ring Circuit which will interpret a 5A FCU Spur for the 2 Lights.
Or to be ultimately safe,
A 10mm SWA from Main CU/40A MCB clipped direct to Outhouse.
Into a 2 Way “Garage” CU with a 16a breaker for Sockets and 6a breaker for lights.
Any doubts or ideas would be great!
Been out the sparky game for a while due to travelling for a couple years and just need best advice! Cheers.
I recently started on my house for an Outhouse/Summerhouse 35m away from main Property.
It requires :-
x5 Double Sockets
x2 Strip Lights
The sockets will be used for Televisions and Charging.
I have 2 ways i’d like to to this.
A 6mm SWA from Main CU/32A RCD clipped Direct to Outhouse.
Onto the back of a 2.5mm Ring Circuit which will interpret a 5A FCU Spur for the 2 Lights.
Or to be ultimately safe,
A 10mm SWA from Main CU/40A MCB clipped direct to Outhouse.
Into a 2 Way “Garage” CU with a 16a breaker for Sockets and 6a breaker for lights.
Any doubts or ideas would be great!
Been out the sparky game for a while due to travelling for a couple years and just need best advice! Cheers.