how the hell do i find a list of cb's/ select them from the OSG ????????? ...or have i just overworked my brain ????????? lol
Off the top of my head i don't think there is a list in the OSG - i always use appendix 3 of BS7671.
edit - oops table 7.1 seems to show them
that q has really baffled me....Is the MCB ratings differnet when talking about 400v/ triple pole ? if so how do i find out which type to use and therefore do the resulting equations become affected ?
Much respect to you Widdler for putting so much time and effort in. One very small point which doesn't affect the outcome at all. The question said
So wouldn't that mean ref method B [42 from table 4A2?] not ref method C, so table 4D2A column 4 = 1.5mm² carries 16.5A
or am i wrong ?:)
Selected reference method was C (No. 57).
In questions where it states within building materials, it refers to direct in masonry. :)
It's all down to interpretation of reference methods, the syllabus I use have in this example gone with the above. But your opinion of reference method B can also be justified.
It's one of the biggest debates I have with my guys.
The question is answered with the exact same approach and formula bar one. The design current (Ib).
With Three phase (400V), we use the following formula:
Ib =
Power (P)
√3xUL
Cheers for the reply, on reflection 57 is probs a better fit :)
I suppose we all have to carry our thermal resistivity meter in our kit as well ;)
Thanks for keeping my brain ticking over!
Ib =
Power (P)
√3xUL
images
Not sure what other posters think but Widdler deserves that for this thread, it was good of you to help that lad out the way you did. Top man
ok here i go :
For deign current : 36.1 A
In : 40A
Ok..... here goes...
Ca : 35 oc...... : factor of 0.94....table 4b1 ?
Cg : 0.82........table 4C1 ???
so ...It = 50.8 A ...????
Im lost as to where i go from here....
I can do the volt drop calc....but i cant suss how to find the correct table for the cable selection ?
Ib -
Ib = Power / SQUARE ROOT of three x Uo = 36.1 A
In = Greater than Ib = 40A breaker
It : = In / Cg = 40 / 0.82 (table 4c1) ......It = 48.78 A
(these values have changed)
Cable : 4mm cable (Table 4G1A , column 9) ?????????????????
If your talking about load balancing over phases.....then....Yeah...kind of...but that would be in the inititial design of the heater itself......not considered during the heater installation...
Seeing as it a three phase supply...You consider that the load in q has already been balanced by the Maker of it.
Installers may need to consider balancing when installing single phase items...into a premesis that uses/ are provided by three phases...( ie,, three single phase (identical heaters) would be installed on a phase each ?
Correct me on this if im wrong though guys..
is that per phase?
The 36.1A figure is the design current for each line (L1, L2, L3) it is not a total value that is then shared between 3 cables if that is what you are asking:)
edit : you have to be a little careful with terminology because the phase current (Ip) only equals the line current (Il) when connected in star. If in delta, as it would most likely be in a motor, then Il = √3* Ip
When designing for cable size it is just the line current that you are interested in.
A complex subject (which i am rapidly forgetting:eek:) but just to be aware that phase current and line current are slightly different and are not always the same value.:)
Much better explanation than mine...:)
Reply to Calculating volt drop, cable selection and mcb selection on an 3kw motor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
8K
Electrical2Go - Electric Car Charging at Home - Comprehensive Guide As EV ownership and the transition towards electric cars rise, having a home...
  • Locked
5K