What about silver coloured plastic conduit lololololol You know you can get it in any RAL colour............................ Sorry............... Normal service will resume!
 
Yes but it's eye wateringly expensive though Archy and I'm not so sure if they're putting it in conduit just yet :)

I bet it is, but when it becomes cost effective, that'll be the death knell for steel conduit.
No more Hilmores, just lads armed with hair dryers! :-)
 
  • Like
Reactions: 2 people
See this is why I don't normally post after visiting the fang farrier...trauma makes me talk nonsense (both mental and financial trauma.....the wallet is still in shock. I'm in the wrong business....get it wrong as a dentist...charge twice....must be the only career where you can get things wrong and still bill the client.....)
Revised plan - go along the lines of what dave suggested - shed is only staying temporarily till I can get the garage erected (10 or 12 feet x 20 feet) and its getting a 40amp supply in 6mm2 3 Core SWA (recovered from the catenary supply I had at the last house, still in perfect nick so getting reused) buried under the gravelled drying area.
 
What about silver coloured plastic conduit lololololol You know you can get it in any RAL colour............................ Sorry............... Normal service will resume!


only used white and black
 
It's not just the fact that the armour is good enough, there's the fact that fault current is unlikely to flow through the external cpc anyway due to the inductive coupling with the armour.
 
I bet it is, but when it becomes cost effective, that'll be the death knell for steel conduit.
No more Hilmores, just lads armed with hair dryers! :-)

I did some conduit today................ Real conduit (20mm Steel)... looks the dogs.. It had a 90 bend and then I had to put a dog leg in because the bloody IT guy stuck is poxy T2 right in the way!

- - - Updated - - -

only used white and black

Good buddy....... you stick with that... At least you won't get a belt off it!
 
  • Like
Reactions: 4 people
There was a period (and probably now) when firms ran an earth wire alongside the swa because they were ignorant and did not know that 99.9 + per cent of the time the armour complied.

Earth wire alongside is waste of time and effort.................dedicated earth core inside swa every time.
Armour can then be back-up earth if required when bonded correctly......... they compliment each other /earth and bond all at the same time........canny Zs reading too :).
 
  • Like
Reactions: 2 people
3 phase motor gets a 4 core too....................so i can put the earth core onto the nice internal earth connection in the motor terminal box that the manufacturers provide:)
 
How much more does it cost to do that? I'd have thought there's going to be a big price difference for adding an extra core, especially when 5core isn't all that commonly used.

Motors is different because you only just flexible cables for the final connection so there isn't a suitable armour.
 
Motors is different because you only just flexible cables for the final connection so there isn't a suitable armour.

Don't know why you would think that mate?
I've taken armoured cable direct to the motor terminal box thousands of times!
 
@ OP. go to jail. do not pass go. do not collect £200. buy some bloody 6mm 3 core SWA. you say you are going to have a garage at a later date. so install to accommodate the additional load you will require then. feed from a non-RCD way in the house CU then install a garage CU in the shed.
 
Why wouldn't you trust it? There's nothing wrong in using the armour as long as it's been correctly sized and the chances of it coming out of a gland are nil as long as it's been done correctly.
What are your thoughts on conduit or trunking as a cpc?

When I was working on big projects, hospitals schools factorys, we had to pull in cpc's, it was spec on conduit work and trucking.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Shed supply
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
46

Thread Tags

Advert

Thread statistics

Created
overskilled,
Last reply from
Bobster,
Replies
46
Views
4,323

Advert