So someone wrapped an intact fuse with foil and it caused a fire due to a faulty appliance ? Is that supposed to be a surprising thing to happen ?
 
Yes.
Unless you wish to blame a fourteen year old.
 
Did you never do that as a kid?
 
All electrical circuits must be protected against 'a small overload of a long duration'!
 
Look at the photos of Grenfell.
The fire originated in a Hotpoint fridge-freezer in flat 16 on the fourth floor. A faulty electrical connection, possibly a loose wire, within the appliance is believed to be the cause.

There was initial confusion and speculation about consumer units (fuse boxes) being a potential cause, stemming from a change in how the London Fire Brigade reported these types of fires.

Actual Cause:
Investigations revealed that the fire started due to an electrical fault in a fridge-freezer located in a fourth-floor flat, specifically a poorly crimped wire connection within the fridge's wiring
 
Last edited:
Yes.
Unless you wish to blame a fourteen year old.
If they did it, and it caused a fire, who would you blame ?.
In England and Wales, the age of criminal responsibility is 10.
 
I would blame you for not learning your trade.
 
All electrical circuits must be protected against 'a small overload of a long duration'.
 
Protecting an electrical circuit from 'a small overload of a long duration' isn't even particularly complicated!
 
All you have to do is compare two figures and make sure that one exceeds the other.
 
Where is the complicated part?
 
Where is the complicated part?
There isn't one.

433.1 Coordination between conductor and overload protective device
Every circuit shall be designed so that a small overload of long duration is unlikely to occur.

So if you want some electrical work done, call a decent electrician who complies with bs7671.
 
Please do not quote legally disclaimed information!
 
433-01-01 A protective device shall be provided to break any overload current flowing in the circuit conductors before such a current causes a temperature rise detrimental to insulation, joints, terminations or the surroundings of conductors. Every circuit shall be designed so that a small overload of a long duration is unlikely to occur.
 
Call an electrician who complies with electrical wiring regulations that have not been legally disclaimed by their authors.
 
Notice how it is written in plain English and tells me what I need to achieve.
That way I don't have to ask you.
 
I think we’ve had enough of this.

I’m locking the threads
 
Status
Not open for further replies.

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cheltenham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Status
Not open for further replies.
Title
Overcurrent protection
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
56

Thread Tags

Tags Tags
protection

Advert

Thread statistics

Created
DWCOCKBURN,
Last reply from
littlespark,
Replies
56
Views
864

Advert