Tapouchoke
Hi guys
I have carried out works on a kitchen, altered cooker cct, altered socket circuit to suit new lay out
Installed rcbos to circuits as they have got socket outlets on them lest than 2oamps
All tested ect
16ml main tails 16ml main earth
now the main gas and water is only 6mml do I have to upgrade this or can I leave it as 6ml and put a comment / departure on the cert as code 4
All comments appreciated good and bad
Cheers