Hi all this is first time I've posted so appologies if I've missed anything out.
Recently just done a i&t and the ring main in one part of the commercial building is completely "ballsed up" to say the least. Spurs off spurs with rings of them and even more spurs off them. Going to have to rewire the ring main.
Only problem is floor area for room is 178m sq. The ring main will be fed by an old bs3871 dorman smith 30a mcb. Type 3 i believe. So needs to be very low zs values.
I know regs say max floor area is 100m sq but with calculations you can have bigger area.
Would a 4mm ring main be ok for this area?
Or would it be best to split it up into separate radials?
Most of the pcs are fed by separate ring so will only be powering few printers an pcs an odd heaters.
I don't have any spare ways on distribution board so if poss will have to keep on the one mcb.
Cables will be run up 1m of trunking then across suspended ceilings.
All your help is much appreciated
Cheers
Recently just done a i&t and the ring main in one part of the commercial building is completely "ballsed up" to say the least. Spurs off spurs with rings of them and even more spurs off them. Going to have to rewire the ring main.
Only problem is floor area for room is 178m sq. The ring main will be fed by an old bs3871 dorman smith 30a mcb. Type 3 i believe. So needs to be very low zs values.
I know regs say max floor area is 100m sq but with calculations you can have bigger area.
Would a 4mm ring main be ok for this area?
Or would it be best to split it up into separate radials?
Most of the pcs are fed by separate ring so will only be powering few printers an pcs an odd heaters.
I don't have any spare ways on distribution board so if poss will have to keep on the one mcb.
Cables will be run up 1m of trunking then across suspended ceilings.
All your help is much appreciated