Hi all this is first time I've posted so appologies if I've missed anything out.

Recently just done a i&t and the ring main in one part of the commercial building is completely "ballsed up" to say the least. Spurs off spurs with rings of them and even more spurs off them. Going to have to rewire the ring main.
Only problem is floor area for room is 178m sq. The ring main will be fed by an old bs3871 dorman smith 30a mcb. Type 3 i believe. So needs to be very low zs values.

I know regs say max floor area is 100m sq but with calculations you can have bigger area.
Would a 4mm ring main be ok for this area?
Or would it be best to split it up into separate radials?
Most of the pcs are fed by separate ring so will only be powering few printers an pcs an odd heaters.

I don't have any spare ways on distribution board so if poss will have to keep on the one mcb.
Cables will be run up 1m of trunking then across suspended ceilings.

All your help is much appreciated
Cheers
 
You are going to have to put your designer hat on here. The sq metre a guide is within a guide and should be dealt with as such, you can have a RING FINAL CIRCUIT of any sq area providing you design it correctly. The major priority for you would be the VD on such a Ring final.

As Spin as indicated you could wire the ring in 4mm or 6mm, if you do decide 6mm is ok then it may be best to wire the 6mm legs into an adaptable box then a single 4mm into the socket if they are going to be BS 1363 socket outlets.

Personally as you have no spare ways in the board I would look at fitting a smaller say 4 way DB. You could either supply this from the old 30amp BS 3871. It will depend on the type of loads that will be utilised in the area, as you say it is commercial you may need to upgrade the 30amp to a 40amp MCB. If it is expected to be a heavier load, then you may be able to supply it another way, perhaps off the existing boards supply.

By fitting a newer DB though will give you much more flexibility in designing a sub installation feeding this area.
 
I was hoping to not have to get out my designer hat in the off chance some one has come across similar issue in past. The client wants me to do it the cheapest way possible.

Think I'll just fit separate board next to original one to feed ring mains an split it up that way.

6mm in sockets is too much trouble for my liking!! Never again after having to get a 90mm 4 core swa into isolation box Designed for 50mm 4core swa.

Cheers for your help everyone
 

Reply to 178m sq floor area for socket outlets in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
782
I'm having a bit of a disaster at the minute and would like an honest opinion. I am having a gas stove fitted in the corner of my room and...
Replies
6
Views
1K
Hi, I want to have installed 2 x 16A commando sockets in my shed. I want to run a MIG welder which has a max output of 180A @ 23V and a 3hp 2.2kW...
Replies
14
Views
5K
Thought I'd seek some advice on something has been frustrating, and the frustration may now be clouding judgement....! It was 30A rewirable fuse...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock