Hi all,

I have a question. 17th edition states my cables need to be at a depth of 50mm or protected by a metallic sheath. The only metallic sheath around is steel conduit, heavy and cumbersome for domestic use. Is there such a thing as metallic channel?

If not, what do you guys use? Seems to be difficult to find a lightweight metallic protector for cables.

Cheers all,

Paul
 
Reg 522.6.7 will tell you that if where you installation is not intended to be of use by a skilled or instructed person, normally domestic, and is installed in accordance of regulation 522.6.6 (v), but not complying with (i) (ii) (iii) or (iv) of that regulation then additional protection by 30mA RCD is required.
 
No. There are 5 options.
1) Bury the cable at a depth greater than 50mm
2) use an earthed metallic sheath (this sheath does not offer mechanical protection, it just provides a fault path if the cable is penetrated by screws or nails)
3) use earthed conduit or trunking
4) provide mechanical protection sufficient to protect the cable from penetration by screws or nails
5) install the cables in safe zones and provide RCD protection.
If this is a circuit for socket-outlets, then you will probablly just want to use RCD protection for the whole circuit.
That way you are protecting both the cables and the socket-outlets at the same time.
 

Reply to 17th edition - cables and cable protection in domestic walls in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there - good site. Mrs wants a new socket directly below a light switch on the ground floor (says it will look neater vertically inline)...
Replies
4
Views
1K
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
899
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
824
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
551

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock