Can anybody help....Trying to establish if I would have to change the mec on a TNS system....

Ok So S=sqr(I2xt)/k

When establishing the value of 't' do I use the characteristics of the distibutors main fuse or the main switch in the CU or I have missed the point entirely?:rolleyes:

And when establishing 'I' do I use 230v or 240v

Some direction in this matter would be most helpful.

Thanks in advance.
 
i think you have to use the value of the main fuse.

use 240v, that is still currently the UK energy providers output voltage, and is likely to be for a long time as they are making more money out of us this way :(
 
Why are you trying to calculate the size of mec when you should be using table 54.7 in relation to meter tails[largest size conductor].
 
Why are you trying to calculate the size of mec when you should be using table 54.7 in relation to meter tails[largest size conductor].

Hi, I don't want to change the existing MEC if I don't have too. So was gonna check if the existing is adequate if not then I'll upgrade them as table 54.7

Thanks for your quick replies....
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Adiabatic Equation
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
3

Thread Tags

Advert

Thread statistics

Created
DYCHE4230,
Last reply from
DYCHE4230,
Replies
3
Views
3,795

Advert