So, I've been trawling through every bit of info available on AMD 3, specifically info regarding non-combustible DBs in domestic premises. Others may have further information regarding the decision made by JPEL/64 as to what was included in AMD 3 following the final draft and I welcome any comments or 'picking apart of' what follows, but it seems quite clear to me that the intent of the regulation is not quite followed through with what is now in print. The last we hear is that within the final draft, 960[SUP]o[/SUP]C glow-wire tested plastic will not meet the requirements of Regulation 421.1.201 and will not be considered non-combustible.

Below is Regulation 421.1.201 in its entirety:

421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:

(i) have their enclosure manufactured from non-combustible material, or

(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12

NOTE 1: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.

NOTE 2: The implementation date for this regulation is the 1st January 2016, but does not preclude compliance with the regulation prior to that date.

Ok, so lets have a look at BS EN 61439-3, the product standard for distribution boards intended to be operated by ordinary persons:

BS EN 61439-3 (Low-voltage switchgear and controlgear assemblies. Distribution boards intended to be operated by ordinary persons) Regulation 10 essentially says that the clause of Part 1 applies (except from a few issues irrelevant to this subject), thus we refer to BS EN 61439-1 (General rules), which says:

10.2.3.2 Verification of resistance of insulating materials to abnormal heat and fire due to internal electric effects

The glow-wire test principles of IEC 60695-2-10 and the details given in IEC 60695-2-11 shall be used to verify the suitability of materials used:

a) on parts of ASSEMBLIES, or
b) on parts taken from these parts

...

The temperature of the tip of the glow-wire shall be as follows:

- 960[SUP]o[/SUP]C for parts necessary to retain current-carrying parts in position;

...

Got that, so let's have a look at BS EN 60695-2-12. This deals with the interpretation of glow-wire test results carried out in accordance with 60695-2-10 and 60695-2-11. It says:

10.1 Test criteria

The test specimin is considered to have withstood this test if there is no ignition, or if all of the following situations apply:

a) the longest sustained flames or glowing of the test specimin after the removal of the glow-wire, t[SUB]R[/SUB], extinguish within 30s;
b) the specimin is not totally consumed; and
c) there is no ignition of the wrapping tissue.

So this essentially tells us that if there is no ignition of the test specimin then the material is fit to be covered by the BS EN 61439-3 product standard. However, it still doesn't quite address whether or not that makes the material non-combustible.

For this reason, we turn to BS EN 13943 (Fire safety vocabulary). Lets look at some definitions:

4.46 combustion
exothermic reaction of a substance with an oxidizing agent
4.186 ignited
caused to be in a state of undergoing combustion (4.46)
4.43 combustible, adj.
capable of being ignited (4.186) and burned
4.239 non-combustible
not capable of undergoing combustion (4.46) under specified conditions

The crux of this matter I think comes down to those aforementioned 'specified conditions'. The fact is, almost any material is combustible if heated hot enough, therefore why does Regulation 421.1.201 not specify these specified conditions?

We can however look at BS EN 61439 which clearly stipulates these specified conditions (the glow-wire test as described in BS EN 60695-2) and it's requirement for plastic domestic distribution boards to pass these tests.

If as per BS EN 60695-2 a material passes the 960[SUP]o[/SUP] glow-wire test through non-ignition, it cannot by definition be called a combustible material, ergo sum - it is non-combustible.

This is of course my interpretation of all these standards and the definitions contained within, I do believe however that this is surely the only way it can be interpreted.

To summarise; if you install a plastic consumer unit within in a domestic property after 1st January 2016, as long as it conforms to the BS EN 61439-3 product standard, by definition, it will be non-combustible. Note 2 within Regulation 421.1.201 giving steel as an example of a non-combustible material is in my opinion nothing more than a red herring.

Hopefully, we might now be able to put this nonsense to bed once and for all!
 
Last edited:
I know this sounds like a crude test, and yes I guess it is.
But I had a spare BASEC 8 way board from Denmans.
Myself and a couple of guys used a blow torch on the poor thing (just for devilment).
It melted and distorted, but it did not combust or catch fire.
And boy did we try.
Ponged a bit though.
 
So, I've been trawling through every bit of info available on AMD 3, specifically info regarding non-combustible DBs in domestic premises. Others may have further information regarding the decision made by JPEL/64 as to what was included in AMD 3 following the final draft and I welcome any comments or 'picking apart of' what follows, but it seems quite clear to me that the intent of the regulation is not quite followed through with what is now in print. The last we hear is that within the final draft, 960[SUP]o[/SUP]C glow-wire tested plastic will not meet the requirements of Regulation 421.1.201 and will not be considered non-combustible.

Below is Regulation 421.1.201 in its entirety:



Ok, so lets have a look at BS EN 61439-3, the product standard for distribution boards intended to be operated by ordinary persons:

BS EN 61439-3 (Low-voltage switchgear and controlgear assemblies. Distribution boards intended to be operated by ordinary persons) Regulation 10 essentially says that the clause of Part 1 applies (except from a few issues irrelevant to this subject), thus we refer to BS EN 61439-1 (General rules), which says:



Got that, so let's have a look at BS EN 60695-2-12. This deals with the interpretation of glow-wire test results carried out in accordance with 60695-2-10 and 60695-2-11. It says:



So this essentially tells us that if there is no ignition of the test specimin then the material is fit to be covered by the BS EN 61439-3 product standard. However, it still doesn't quite address whether or not that makes the material non-combustible.

For this reason, we turn to BS EN 13943 (Fire safety vocabulary). Lets look at some definitions:






The crux of this matter I think comes down to those aforementioned 'specified conditions'. The fact is, almost any material is combustible if heated hot enough, therefore why does Regulation 421.1.201 not specify these specified conditions?

We can however look at BS EN 61439 which clearly stipulates these specified conditions (the glow-wire test as described in BS EN 60695-2) and it's requirement for plastic domestic distribution boards to pass these tests.

If as per BS EN 60695-2 a material passes the 960[SUP]o[/SUP] glow-wire test through non-ignition, it cannot by definition be called a combustible material, ergo sum - it is non-combustible.

According to BEAMA, this will still not pass.

This is of course my interpretation of all these standards and the definitions contained within, I do believe however that this is surely the only way it can be interpreted.

To summarise; if you install a plastic consumer unit within in a domestic property after 1st January 2016, as long as it conforms to the BS EN 61439-3 product standard, by definition, it will be non-combustible. Note 2 within Regulation 421.1.201 giving steel as an example of a non-combustible material is in my opinion nothing more than a red herring.

Hopefully, we might now be able to put this nonsense to bed once and for all!

Cheers
 

BEAMA don't write the rules, and even if they did, it isn't in the rules. It's one thing making your intent clear when working on legislation, but unless you illustrate that intent in the actual regulation it refers to, then the intent becomes irrelevant.
 
Purely for your enjoyment on this Thursday night, I read the latest issueing from the IET Wiring Matters earlier, ....

I quote, "There is no published definition for the term ‘non combustible’ that aligns with the intent of Regulation 421.1.201."

So, if the material is undefined, one can use anything one likes?!?!?
:smilielol5::smilielol5::smilielol5:
 
Damien,

This is the crux of my comments over the last few months.

The "metal" bit comes from BEAMA & their members deciding that ferrous metal is the only material that meets the intent of the regulation.

This I have always disagreed with.

Why is an installation standard interfering with a product standard?...
 
Metal consumer unit for TT,

this podcast from the IET tells you of requirements of if you need to protect your tails, db, etc with rcd here.

Wiring Matters podcast series - IET Electrical
 
So, I've been trawling through every bit of info available on AMD 3, specifically info regarding non-combustible DBs in domestic premises. Others may have further information regarding the decision made by JPEL/64 as to what was included in AMD 3 following the final draft and I welcome any comments or 'picking apart of' what follows, but it seems quite clear to me that the intent of the regulation is not quite followed through with what is now in print. The last we hear is that within the final draft, 960[SUP]o[/SUP]C glow-wire tested plastic will not meet the requirements of Regulation 421.1.201 and will not be considered non-combustible.

Below is Regulation 421.1.201 in its entirety:



Ok, so lets have a look at BS EN 61439-3, the product standard for distribution boards intended to be operated by ordinary persons:

BS EN 61439-3 (Low-voltage switchgear and controlgear assemblies. Distribution boards intended to be operated by ordinary persons) Regulation 10 essentially says that the clause of Part 1 applies (except from a few issues irrelevant to this subject), thus we refer to BS EN 61439-1 (General rules), which says:



Got that, so let's have a look at BS EN 60695-2-12. This deals with the interpretation of glow-wire test results carried out in accordance with 60695-2-10 and 60695-2-11. It says:



So this essentially tells us that if there is no ignition of the test specimin then the material is fit to be covered by the BS EN 61439-3 product standard. However, it still doesn't quite address whether or not that makes the material non-combustible.

For this reason, we turn to BS EN 13943 (Fire safety vocabulary). Lets look at some definitions:






The crux of this matter I think comes down to those aforementioned 'specified conditions'. The fact is, almost any material is combustible if heated hot enough, therefore why does Regulation 421.1.201 not specify these specified conditions?

We can however look at BS EN 61439 which clearly stipulates these specified conditions (the glow-wire test as described in BS EN 60695-2) and it's requirement for plastic domestic distribution boards to pass these tests.

If as per BS EN 60695-2 a material passes the 960[SUP]o[/SUP] glow-wire test through non-ignition, it cannot by definition be called a combustible material, ergo sum - it is non-combustible.

This is of course my interpretation of all these standards and the definitions contained within, I do believe however that this is surely the only way it can be interpreted.

To summarise; if you install a plastic consumer unit within in a domestic property after 1st January 2016, as long as it conforms to the BS EN 61439-3 product standard, by definition, it will be non-combustible. Note 2 within Regulation 421.1.201 giving steel as an example of a non-combustible material is in my opinion nothing more than a red herring.

Hopefully, we might now be able to put this nonsense to bed once and for all!

D, thank you very much for bringing together the relevant standards in one place for analysis. Not withstanding the view that the changes to BS 7671 regarding electrical enclosures for the domestic market are an exercise in both treating the 'symptom rather than the cause' and 'shutting the stable door after a bolting horse', I comment only on the conclusions that you draw.

According to your text BS EN 60695-2-12 states:


10.1 Test criteria


The test specimin is considered to have withstood this test if there is no ignition, or if all of the following situations apply:


a) the longest sustained flames or glowing of the test specimin after the removal of the glow-wire, tR, extinguish within 30s;
b) the specimin is not totally consumed; and
c) there is no ignition of the wrapping tissue.


10.1 a) indicates that the test specimen may ignite but must be self-extinguishing within 30s.


Clearly this is not 'non-combustible'. You also rightly state:


'If as per BS EN 60695-2 a material passes the 960o glow-wire test through non-ignition, it cannot by definition be called a combustible material, ergo sum - it is non-combustible.'


This is true; however, a plastic enclosure could also pass the standard through the less strict route of 10.1 a), b) and c).


Therefore, without manufacturers' publishing the results of their testing regime to demonstrate compliance with BS EN 60695-2, the installer will not know whether an enclosure compliant with the standard achieved compliance by being truly non-combustible or by being self-extinguishing. Thus the changes to BS 7671 apply a more restrictive requirement than BS EN 61439-3.
 
As a follow up to post 3,
Thought it worth a mention that the board I referred to is rated as;

Self-extinguishing ABS
IP2XC
BSEN 61439-3

And this is the spec most plastic CU's follow.
Now if they are compliant with the new AMD 3 then the metal clad board scenario is nothing more than a red herring.

If not !!
Then there are a lot of boards out there that, not only are no longer compliant.
But also constitutes a fire hazard ??
Surely this will open up a completely new can of worms when conducting EICR's

This isn't simply a case of non compliance, as per installed to an older version of BS7671 which may or may not receive a code 3

But a case of all plastic consumer units constituting a fire hazard, and therefore legitimately receiving an automatic code 2 (unsatisfactory result)

I just cant see that being allowed to happen ????
 
the whole issue is a storm in a teacup. will it affect the price of beer.... NO.... therefore it can be ignored.
 
manufacturers will soon have plastic CUs that conform to 421.1.201, and cef will have a nice little sideline in yet another shiny sticker to add to the ones alreasdy adorning the CU.
 
As a follow up to post 3,
Thought it worth a mention that the board I referred to is rated as;

Self-extinguishing ABS
IP2XC
BSEN 61439-3

And this is the spec most plastic CU's follow.
Now if they are compliant with the new AMD 3 then the metal clad board scenario is nothing more than a red herring.

If not !!
Then there are a lot of boards out there that, not only are no longer compliant.
But also constitutes a fire hazard ??
Surely this will open up a completely new can of worms when conducting EICR's

This isn't simply a case of non compliance, as per installed to an older version of BS7671 which may or may not receive a code 3

But a case of all plastic consumer units constituting a fire hazard, and therefore legitimately receiving an automatic code 2 (unsatisfactory result)

I just cant see that being allowed to happen ????

The point is, if a plastic board is combustible, then it doesn't conform to the product standard and therefore shouldn't have been installed in the first place. Believe you me, there are an awful lot of boards out there that fall way short of the product standard! Some even made by BEAMA member companies. This needs addressing.

The product standard is fine, the installation standard was fine before it tried to meddle. Sort out the products that don't meet the product standard and sort out the installers that don't meet the installation standard and whoopty doo, what do we get as a result? Zero fusebox fires!
 
Good work Damian, this amendment really is a load of BS....!

At a slightly different angle, what if a plastic CU that is deemed combustible is installed after 2016 upon the proviso it will be being housed in a fire rated/non combustible enclosure. Do we need to have the enclosure installed first... Bit of the old chicken and egg going on. Are we expected to be buying steel shells to house them.

I read on Contactums website last night, in the FAQs I think, that existing plastic CUs are not unsafe and do not need to be replaced with metal. Well that's stating the jeffing obvious....so no amendment needed then after all.

All that is needed is a moral and diligent work ethic and less limp-wristedness. Market forces are partly to blame in the rise of the cowboy installation. I say the schemes should enforce extra supervision and training for any body found responsible for a fire. Not so easy though me thinks.

I do prefer plastic CUs over metal any day of the week.... Or is that 47 weeks and counting!

I wonder if the manufacturers prefer to sell metal CUs as it may be more profitable. They don't seem to be fighting the wording/semantics/interpretation of the reg at all.
 

Reply to AMD 3 - Hopefully busting the myth of metal DBs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top