True, got one at home.
Seem pretty crappy though, Two tiny plastic pins to lock the switch off.

True, but if someone is going to make efforts to turn it on by breaking those pins, and ignoring the huge red flappy thing with a padlock dangling off it, then no amount of safeguarding and locking off is going to protect you from that person.
 
On the legal standing of the BGB, I’m not a lawyer, but the Building Regulations are law, which everyone agrees on, and the approved documents give guidance on complying with them.

The following is an extract from Approved Document Part P 2013 Edition, Section 1 Design and Installation (Page 3)
“General
1.1 Electrical installations should be designed and installed in accordance with BS7671:2008 incorporating Amendment No.1:2011.
So does mean that the BGB, is in a roundabout way, law?

Going back to the thread subject bathroom fans, fuses and isolators.

Change the pull switch controlling the lights to a DP pull switch (MK and Crabtree do them), connect the lighting feed and sw/wire to one pole.

From the lighting circuit take a Live and Neutral to a Fused Spur (fused to 3A).

Then run a twin from the spare pole of the pull switch to the spur.

Run a 3c to the fan.

Connect the lives from the 3c and the twin to the switch into the Load of the spur.

Joint the sw/wires from the twin and 3c in a Wago in the back of the Spur box.

If you really want to install a 3 pole isolator, run 2 twins and the 3c to it and make the connections there.

Both lives fused and isolated...
 
Sorry, can't agree with any of that last paragraph or not...you are saying that no isolation is required close to the fan and then that no 3 pole device is required for isolation. Ever tried changing a fan on RCD protected circuit? you are really saying that you can remove all the connections, in most cases with permanent live and switched without causing the RCD to trip? TN system or not who takes the chance? Just because you interpret the regs your way doesn't make it correct does it?

I awlays fit a FCU fused to manufactures requirements and a 3 pole isolator and always 3+cpc cable and all accesible (usually above doorway).
I really can't believe some of the comments here concerning providing BS fuses protection to both permanent live and switched live, I would consider that wiring knowledge as 1st year stuff...
 
you are saying that no isolation is required close to the fan and then that no 3 pole device is required for isolation.

Just because you interpret the regs your way doesn't make it correct does it?

Find me some regulations then that prove me incorrect. If you can, I'll happy eat humble pie, until then why not keep your arrogant remarks to yourself.

And guess what, the beauty of non-statutory regulations is that they ARE often open to interpretation.
 
I really can't believe some of the comments here concerning providing BS fuses protection to both permanent live and switched live, I would consider that wiring knowledge as 1st year stuff...

Not sure if I have misunderstood your quote, so appologies before i get shouted at, manrose fans installation wiring diagram show an FCU with a live split, 1 to light switch for switching and one direct to the fan as permanent live.
What puzzled me and this has now been answered within this thread was the small DP pull cord, one for fan switch live and one for light switch live. Haven't seen one for years and certainly my usual supplier said he had never seen one for years only the big shower switch.

If you follow the wiring logic above would that not do away with the need for the triple pole? Both feeds for the fan are through the fuse which can be removed and the fuse carrier locked open for safe isolation so regardless of location safe isolation is satisfied?

That will be my preferred route from now on, so now to shout at my supplier as I want DP 6 amp pull cord light switches.

Thank you Mr Skelton, for all we have had our disagreements the discussion you started has at least give me a standard which I am happy with and which has puzzled me for months if only it hadn't taken so long! The last fan wiring diagram would never have worked and all statute says that manufacturers instructions should be complied with - and that p!sses me off.
As a footnote, including myself, sometimes when writing briefly not all the meaning comes across. I know what I want to say but sometimes when I read back not even I understand it!
 
To answer gonefishings' post #56 In my last post #54 I wasn't saying install or not install a 3 pole isolator, I mean't, it's up to your interpretation of the regulations whether to install one or not. All I was offering was a solution to the problem of fusing the Switch feed to the fan.

If you're changing the fan on a RCD protected circuit and it's wired through a Spur as my original post and the spur is switched off then then the neutral to the fan is isolated.

The DP Pull Switch is 16A, MK3151WHI or Crabtree 2163 or Legrand 061130

Discount-electrical.co.uk sell the MK
 

Reply to Bathroom extractor fans and 3 pole isolation: A source of much controversy in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
9K
Hi to all, If extractor fan in bathroom is autonomous does it still require isolator switch or usual fused switch will do? It runs of 12v...
Replies
5
Views
3K
Part 1. I Have 2 red wires and one brown going into my ceiling pull chord UK light switch in bathroom. BROWN AND RED into L1 and RED into COM...
Replies
1
Views
1K
Hi there. Recently our bathroom extractor fan broke, so I got a new one but I'm having difficulty wiring it (homeowner DIY guy here). So... there...
Replies
6
Views
3K
Hi, The house I've moved in to doesn't have an extractor in the main bathroom so I'm looking at placing an inline extractor in the attic directly...
Replies
5
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock