I’m not taking a “side” in this rather heated discussion, feeling that, as with a lot of the content in the BGB, isolation is left rather open to interpretation, by different people.
Here are a few extracts from various manufacturers installation leaflets. Apologies if the images don't turn out quite right, it's my first attempt at this...
Greenwood Airvac – Unity CV100
Greenwood Airvac – EL100, EL150U, EL150 & EL150SCPC
Vent Axia
Manrose
Xpelair
Out of the 4 manufacturers only one mentions a 3 Pole isolator and this is in addition to the suitably fused connection unit, which are all double pole. I think, if you lock the fuse carrier open, then it would be unlikely that some one would switch the spur on, maybe causing you a problem with the RCD, if you are changing the fan.
On the same subject, by my user name you can tell I'm primarily, nowadays an estimator, but I am time served and had a break from office work for a while, a few years ago and “went back on the tools”. I price a lot of jobs, mostly commercial with some apartment blocks and a lot feature extract fans fed from local lighting circuits and it’s 50/50 on whether a FCU or both a FCU and fan isolator is required. Most of the jobs are pre-designed by "experts"
Here are a few extracts from various manufacturers installation leaflets. Apologies if the images don't turn out quite right, it's my first attempt at this...
Greenwood Airvac – Unity CV100
Greenwood Airvac – EL100, EL150U, EL150 & EL150SCPC
Vent Axia
Manrose
Xpelair
Out of the 4 manufacturers only one mentions a 3 Pole isolator and this is in addition to the suitably fused connection unit, which are all double pole. I think, if you lock the fuse carrier open, then it would be unlikely that some one would switch the spur on, maybe causing you a problem with the RCD, if you are changing the fan.
On the same subject, by my user name you can tell I'm primarily, nowadays an estimator, but I am time served and had a break from office work for a while, a few years ago and “went back on the tools”. I price a lot of jobs, mostly commercial with some apartment blocks and a lot feature extract fans fed from local lighting circuits and it’s 50/50 on whether a FCU or both a FCU and fan isolator is required. Most of the jobs are pre-designed by "experts"