The pump has been changed as has the fan so I'm not sure if it's that.

I also disconnected the thermostat so it is running all of the time as long as the boiler is on and it had the same result.

If it is on 3 I and I turn it up it takes around 10 mins to trip, and it takes the same time it it's done from a cold start.
 
I have seen exactly this fault. C/H would fire up and about 5 mins later the lighting circuit would trip. Long straight run of copper pipe, expanding a few mm and pressing on a cable that was laying beside it in a joist notch. A long shot I agree but possible. In this case, though, it would have to be one of the heating system cables, because the tripping occurs when the heating system FCU is on and not otherwise (e.g. post 4).

Lucian, he does say RCD trips so it could be affecting any circuit.
 
The only way you are going to find this fault is by unplugging / isolating every thing in the property , Main Switch off and by pass the respective RCD (temporary) Main switch back on then switch on the boiler bring it up to temperature , using a clamp meter that measures in MA on each off the CPCS in turn ,bear in mind no other person is to use any equipment in the property whilst doing this , you can then trace this back
 
Lucian, he does say RCD trips so it could be affecting any circuit.

But he says that turning the heating FCU off stops the tripping and it can trip instantly when you turn it back on, even before the boiler fires up. So this suggests the FCU is isolating the fault, i.e. it's in the heating wiring.

using a clamp meter that measures in MA on each off the CPCS

If the fault is to the heating pipework or boiler casing, this probably won't find it, as most of the current won't be going through the CPC. Much better to measure the difference in the L&N, which is after all what trips the RCD.
 
Agree , this might not find it , its a difficult one this as it could be going back through the casing as you say , I would eliminate all other possibilities though with other wiring on other circuits though , I suppose you could throw out a temporary supply from the consumer unit just to supply the boiler on its own , with all other circuits isolated
 
Consumer unit tails: the two thick grey cables, that supply the consumer unit, from the meter. Line & neutral.
 
Agree , this might not find it , its a difficult one this as it could be going back through the casing as you say , I would eliminate all other possibilities though with other wiring on other circuits though , I suppose you could throw out a temporary supply from the consumer unit just to supply the boiler on its own , with all other circuits isolated

I disconnected the cooker and used an extension lead to supply the boiler and it had the same result. I also isolated all other circuits on the rcd whilst I tested it.

the circuit would also not reset until I unplugged the boiler.

I've called Worcester again and they are coming out on Wednesday.

Fingers crossed.

Thanks everyone for your help so far
 
Is the boiler circuit direct from the consumer unit or part of another circuit ?, is it a rcd or a rcbo that is tripping, if its the main switch then it will be a rcd if its replaced the mcb it will be a rcbo
 
So I put the boiler on a non rcd circuit and the rcd still tripped when the boiler was put on anything above 3.


I'm guessing one of the pipes is causing the wiring to heat up and trip, now it's just a case of finding it!


The sockets are on a ring circuit, is there anyway to isolate one room at a time so narrow down where the issue could be?
 
We seem to have some conflicting evidence. In posts #4 & #27 the fault appears quite certainly to be in the heating wiring, because switching off the FCU (#4) or unplugging the C/H system (#27) immediately stops the tripping, reconnecting it can cause an instant trip (#4) even without the boiler firing. Now you have moved the C/H circuit to a non-RCD CU way and the behaviour hasn't changed. At least one RCD-controlled circuit must be faulty, which can't be the boiler wiring.

Putting the two together, how about a cross-connection between the boiler wiring and another circuit, such as borrowed neutral that passes current when a stat changes over or thermally-triggered short? Well, then we have the conundrum that when the two circuits were both on the RCD originally, then unless there are multiple faults (involving a live from each circuit and a CPC) the original fault would not have caused a trip.

So it's looking like either one or more of your observations is wrong, there's a general snarl-up somewhere, or there might be two separate faults, one on a circuit that is still RCD-protected and the other a cross-connection, borrowed neutral etc. on the C/H wiring.

I fear you are going to have to get real test results to take it further without a whole load of possibly dangerous trial and error. I would be tracing strategically with a leakage clamp, insulation tester etc, taking in certain permutations (e.g. N-N between circuits) that a routine quick test would not. I would also by now have disconnected all the heating wiring from the boiler and meggered the hell out of it!
 
Last edited:
I think this is a troll

Gets an electrician in to check out the wiring in the first post then in later posts appears to be doing the electrical work himself
 
So I put the boiler on a non rcd circuit and the rcd still tripped when the boiler was put on anything above 3.


I'm guessing one of the pipes is causing the wiring to heat up and trip, now it's just a case of finding it!


The sockets are on a ring circuit, is there anyway to isolate one room at a time so narrow down where the issue could be?

If and when you get a spark in, tell them what you've been doing!

Madness.
 
Shall we eliminate some possibilities?

1. Heat... well, on a modern boiler a rad loop tends to run (maxed out) at no more than around 75C, and a DHW feed at around 65C as they leave the boiler... neither of which temperatures are going to cause a cable, or a 15mm copper / plastic pipe many issues, even if they were touching side by side.

2. OP - as you paid for an electrician to come in and do some tests, he should have left you with some paperwork - post it up.

3. If a Worcester engineer, who only ever in his life sees and touches Worcester boilers and knows each part individually by his pet name for it, say's it's not their kit at fault, I'd be inclined to pay attention to it.
 
Shall we eliminate some possibilities?

1. Heat... well, on a modern boiler a rad loop tends to run (maxed out) at no more than around 75C, and a DHW feed at around 65C as they leave the boiler... neither of which temperatures are going to cause a cable, or a 15mm copper / plastic pipe many issues, even if they were touching side by side.

2. OP - as you paid for an electrician to come in and do some tests, he should have left you with some paperwork - post it up.

3. If a Worcester engineer, who only ever in his life sees and touches Worcester boilers and knows each part individually by his pet name for it, say's it's not their kit at fault, I'd be inclined to pay attention to it.

Mine is running at 80 degrees C on the flow leg (as it leaves the boiler) and can - if I wind it up - reach 90 degrees C .. so there !! nernernenerner!! :ciappa:
 

Reply to Boiler & RCD Issue in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Calling all electrical professionals / boiler tradesmen -WE NEED YOUR HELP! Every so often (twice in the last two days) when running the hot...
Replies
15
Views
364
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
473
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
453
Hi, I’d really appreciate some advice or suggestions as to what could be causing an ongoing issue I have with my RCD tripping. My RCD trips when...
Replies
1
Views
849
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock