I would always consider galvanised trunking and conduit containing low voltage cables to be an exposed conductive part. (Likewise the armour of an SWA.) It's not the same scenario as cable tray which is not intended to be used with non-sheathed cables.
I would always consider galvanised trunking and conduit to be an exposed conductive part. (Likewise the armour of an SWA.) It's not the same scenario as cable tray which is not intended to be used with non-sheathed cables.
I never said non sheathed cables I said sheathed
I know. I pointed out that comparing trunking/conduit with tray is wrong as tray is not intended to be used with non-sheathed cables whereas trunking and conduit are.
I think the op is saying twin and earth cables installed in conduit and not singles.
Singles would always need containment and if metallic then always earthed as it only has one layer of insulation (basic protection) only
I am aware of that. I am saying that the fact that trunking and conduit are designed for non-sheathed cables means that they must always be regarded as exposed conductive parts. I am aware that singles aren't being used in the conduit in this instance. (T&E in conduit is generally something to be avoided to be honest, as that isn't what conduit is designed for. I accept that sometimes it is handy to improve the look of drops or provide extra mechanical protection or whatever though.
T&E also only has one layer of insulation though - the insulating properties of the sheath are not the same as the insulation and it is only there to provide mechanical protection.
But it would take the basic insulation to fail and the sheath to fail for it to become a hazard not taking impact into account.
Rather than people saying it’s metal it must be earthed my interpretation is not necessarily if using cables such as twin and earth.
my tuppence worth. similar scenario is metal tray/basket carrying T/E. that tray/basket does not have to be earthed.
Because I guess the tray isn’t part of the electrical installation that’s to say it’s not classed as an exposed conductive part it’s only a cable management system.
If you have GN8 I’d have a read of page 164&165.
I have earthed basket and tray many times before to follow specification.
so. up aladder checking for a damaged cable. one hand in contact with the esrthed tray. other hand fishing round contacts a live conductor ( insulation damage?). ZAP.
Usually through parallel paths the basket ends up earthed anyway such as metal framed structures when you mount the brackets to them.
Got a belt off a tray with T&Es on it in a ceiling void a few years back. One length run across the void and was isolated from any earth. The cables dropped through the perforations with no protection and one must have been cut through because the tray was live which I discovered when I provided a path for it to the ceiling grid, never say never.
I asked a similar question of Elecsa a couple of years ago regarding T&E running through a backbox to identify a drop, before going through a wall. They told me that as long as the T&E is continuous, then the backbox does not need to be earthed, as the cable is insulated and sheathed.
Reply to Bonding of conduit in kitchen floor in the UK Electrical Forum area at ElectriciansForums.net
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...