J

jimjamjimajam

Hi guys. Am changing a consumer unit but the property has no equi bonding to incoming water. Usually I would make sure it is installed but from where the supply is would be a big job to put it in.
Can I still sign my work off and note that it's been advised or do I insist that the customer pays for the work involved?
 
Im pretty sure you cant go ahead with the cu change. I have this all the time. I got a leaflet off the niceic to back me up when i tell the customers. Check with your provider. That way then you can always show the customer the email.
 
Luke is right, big NO, NO!!

If you are doing a consumer unit change then equipotential bonding MUST be in place to satisfy the requirements of protective measures for automatic disconnection of supply. (Somewhere in Part 4 of the BGB)

No bonding, no consumer unit change Im afraid!
 
  • Like
Reactions: 1 person
As above, it must be installed.
Quote the customer for the board swap with bonding and leave it with them. Inform them that any cheaper quote that excludes bonding will be against regulations, and ignoring key safety measures.
 
  • Like
Reactions: 1 person
if you've already done the change then you're buggered, you'll have to do it for nowt if they wont pay.
 
  • Like
Reactions: 1 person
It has to be done and if you've already changed the cu, i suggest you do it for free otherwise it'll reflect badly on you, they won't be happy and just think you're after more work , always test for things like this before quoting! Although is the water run in plastic?
 
Every estimate I do for a CU change includes line items for installing/upgrading bonding, another for replacing the tails and finally a caveat that if faults are found additional time, materials and costs may be incurred.

Never had a complaint yet about presenting the information in such a way, this is because I explain it all when I visit.

How anyone can say that they quote for a CU change and not include the bonding is a fool.
 
Last edited by a moderator:
  • Like
Reactions: 1 person
can you not pick up water any closer than stop cock then test and record it. not great but would get you out a hole
 
We need more fun in life.

demongreen 003.jpg


We do! :-)
 
Hi guys. Am changing a consumer unit but the property has no equi bonding to incoming water. Usually I would make sure it is installed but from where the supply is would be a big job to put it in.
Can I still sign my work off and note that it's been advised or do I insist that the customer pays for the work involved?
if you dont know the answer to this....then you`v got no business carrying out works on peoples electrical installations...
what a load of complete incompetant twaddle this is....
 
  • Like
Reactions: 1 person
Had a shufty at newly renovated house last year or so ago.
Plastic pipe coming in, brass stop cock, plastic pipe off to the rest of the house.
One guess... :smilielol5:
 
Here's the question nobody has asked yet..... Is the water supply pipe plastic?

Yes, but we still have a few who argue that even with the incomming supply in plastic, if the internal pipework is metallic, they still insist on installing protective bonding, even with testing to see first.

My personal preferance is to to any incoming services and install accordingly.
 
Yes, but we still have a few who argue that even with the incomming supply in plastic, if the internal pipework is metallic, they still insist on installing protective bonding, even with testing to see first.

My personal preferance is to to any incoming services and install accordingly.
It would need testing in this instance to see if it introduces a potential, what gets me is when the incoming is plastic and the whole install is plastic yet some posts on here say that they would still insist on a small length of copper by the stop tap to bond to? Seems a pointless waste of copper to me
 
yep. should all be given to wet-pants to make a complete waste of it.
 
  • Like
Reactions: 1 person
Main protective equipotential electrical safety connection earth bonding conductor cables.
I believe is the correct term :smilewinkgrin:
Thats a great thing to say to customers! It sounds expensive and worthwhile whereas just "bonding" sounds as if it should cost 10 shillings and is not important :D
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
c/u change no Equipotential bonding
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
jimjamjimajam,
Last reply from
Andy78,
Replies
25
Views
2,566

Advert