As above really, just want to double check something.
10.5kW shower, 20m run, under floorboards in insulation, 10mm t&e.
Ib=10500/230 = 45A
As most of the run is in insulation, Ci factor is 0.5, so It must be greater than Ib/0.5
So basically I need a cable with 90A capacity under ref. method C to allow for all the insulation.
Ref method 100 (under less than 100mm of insulation) shows 10mm cable having a CCC of 45A.
Can someone please explain why the difference and what I'm missing? There must be a paragraph in the regs I've overlooked. The CCC table doesn't have any diversity applied to they so I don't get the drop.
Is it that ref method 100 assumes cable has one side touching plasterboard and one side in insulation, and calculating using figures above give the requirements for a cable completely surrounded by insulation?
So;
Clipped direct (Ref method C) - 64A
Ref method 100 - 45A (45/64 = rating factor of 0.7 from Ref method C)
Surrounded by insulation - factor of 0.5.
This means that to get the cable rating above 90A under ref method C would need a 25mm cable!!!
Cheers
10.5kW shower, 20m run, under floorboards in insulation, 10mm t&e.
Ib=10500/230 = 45A
As most of the run is in insulation, Ci factor is 0.5, so It must be greater than Ib/0.5
So basically I need a cable with 90A capacity under ref. method C to allow for all the insulation.
Ref method 100 (under less than 100mm of insulation) shows 10mm cable having a CCC of 45A.
Can someone please explain why the difference and what I'm missing? There must be a paragraph in the regs I've overlooked. The CCC table doesn't have any diversity applied to they so I don't get the drop.
Is it that ref method 100 assumes cable has one side touching plasterboard and one side in insulation, and calculating using figures above give the requirements for a cable completely surrounded by insulation?
So;
Clipped direct (Ref method C) - 64A
Ref method 100 - 45A (45/64 = rating factor of 0.7 from Ref method C)
Surrounded by insulation - factor of 0.5.
This means that to get the cable rating above 90A under ref method C would need a 25mm cable!!!
Cheers