Today I used a Fluke voltage meter on a couple of 30mA ABB RCD 's to see if there was any voltage coming out it tripped out now it doesnt trip when testing on my megger MFT 1552. Could I have damaged them with the voltage tester ?

Many thanks Danny
 
dont have the fluke meter myself but if it has other settings that you went through while leads were in place you may have damaged it or if you carried out the wrong test accidently
Dont forget to check your mft 1552 is ok an a known working rcd just to rule out this possibility
 
Today I used a Fluke voltage meter on a couple of 30mA ABB RCD 's to see if there was any voltage coming out it tripped out now it doesnt trip when testing on my megger MFT 1552. Could I have damaged them with the voltage tester ?

Many thanks Danny

If you have the instruction booklet for the voltage tester see how much current it draws, had similiar problems with voltage tester every time it was because the test instrument draw 15mA, that why I use martindale GS 38 voltage tester now that only draws 5 mA max.

You tester could be drawing sufficient current to cause the RCD to trip.
 
But if this is the case, if there was an rcd main switch (more likely 100mA), surely if you tested for voltage on any circuit fed through it, it's possible that the rcd would be damaged. Don't understand:confused:.
 
But if this is the case, if there was an rcd main switch (more likely 100mA), surely if you tested for voltage on any circuit fed through it, it's possible that the rcd would be damaged. Don't understand:confused:.

Your original question stated that you tested a 30 mA RCD, which I answered, that some test meter and voltage indicator draw 15mA or more to function, and this is sufficient current to cause nuisance tripping of RCD.

As a result when I bought a GS38 voltage indicator I chose one that only requires 5mA for it to function.

Check you manual or search the internet to see what current you tester etc draws.

Where does the 100 mA comes from ? can not help if you move the goal posts.
 
Today I used a Fluke voltage meter on a couple of 30mA ABB RCD 's to see if there was any voltage coming out it tripped out now it doesnt trip when testing on my megger MFT 1552. Could I have damaged them with the voltage tester ?

Lets get back to the original question. The basic answer is that you may well trip the RCD if you test line to earth or nutral to earth (depending, as stated above, on the current drawn by your voltage tester) That is not the point. The question you ask is could you have damaged the RCDs. The answer is not with a voltage tester.

You can however seriously damage an RCD with an Insulation Tester. RCDs must be disconnected before making an insulation test on any circuit connected to them.
 

Reply to Can a voltage meter damage an RCD ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

i need to purchase a voltage proving unit - i have seen Megger MPU690, Martindale PD690, and Socket and See SP400, and Fluke but difficult to...
Replies
2
Views
439
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
378
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
360
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
579
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
842

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock